He has a right to be as particular as he wants, but you don't have ANY
first-hand knowledge of what transpired, gauge accuracy, etc. and Bill is
right to suggest a short and simple letter leaving other possibilities open.

Murphy notes that otherwise you may have injury added to insult when YOU get
a letter from the numnut's atty advising you're being sued for libel.

Or, load it up and sign Bill's name!- 

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest Wilson
Sent: Friday, February 27, 2009 10:49 AM
To: [email protected]
Subject: Re: system review

But this is his home Bill. He has a right to be more demanding.  
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: [email protected]

Date: Fri, 27 Feb 2009 08:33:47 
To: <[email protected]>
Subject: RE: system review


Step 1 - Do not send an overnight letter to the fire marshal.

Step 2 - Do send an overnight letter to the building owner.  Make it
simple so you don't do any engineering or make any assumptions about who
didn't do what when.

Dear mr/ms owner; on a recent visit i noted the required automatic
sprinkler riser pressure is more than the available city pressure
showing on your pressure gage. you should look into this matter by
contacting your design engineer and/or sprinkler contractor. perhaps
your pressure gage is in error, the system hydraulic data is incorrect,
or there may be a problem with the water supply.  if the pressure gage
is accurate and the stated system pressure requirement is correct, your
sprinkler system will not operate as it was designed.

(My name is below, but use yours instead)

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: system review
From: "Garth W. Warren" <[email protected]>
Date: Fri, February 27, 2009 9:31 am
To: <[email protected]>

Question for the lettered members and others with experience and/or an
opinion -

I recently looked at the riser of a new system installed in my home
town.
The system requirement according to the hyd. calc. nameplate states
377.9...@75psi. The system gages read 60psi static.
When I contacted the water superintendent he stated the installing
contractor took the hydrant flow information used to design the system.
He
also stated that he head been asked to have the standpipe full and to
have
both Town pumps turned on before the hydrant was flowed.
He continuede that it is standard procedure to have a water department
employee respond to the water plant for every fire department discharge
to
turn on the pumps. He stated the standpipe is filled once weekly prior
to
weekends so that water employees do not have to work weekends then the
standpipe is drawn down, filled during the week.....
It appears the "best case scenario" was used in taking the hydrant flow
making the system suffient only when the standpipe is filled and both
pumps
are in operation.
I do not see anything in 13 which tells anyone how to determine the
acceptability of hydrant flow data, however if the gauge states there is
15
pounds less static pressure than what is required residually for the
system
to operate - then there is a problem.
Is there any requirement for engineers or others to apply acceptability
standards to hydrant flow data or can the results purposely be slanted?
It
seems the system will operate properly Thursday 10am through Friday at
4pm.......
The local AHJ states he accepted the opinion and acceptance of the
engineer
hired to review and accept the system. I do not know if this firm or
individual has any training in fire protection systems, or if he has
provided any such credentials to the AJH. This is in the State of NY.

opinions? thoughts? code references? standard references?

thanks in advance,
Garth
retired fitter


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to