Pardon me if this is ground that was already covered-

I specify the Inspector's test Connection to be located at the sprinkler riser. 
This is NOT something that is new to NFPA-13 either.  E.g., the 1996 edition 
(4-15.4.2) does not require the location to be at the riser - it doesn't 
specify any particular location. Commentary in the handbook that year 
specifically states that the purpose of the connection is to "verify the 
operation of the water flow alarm device(s)." The appendix dialogue recommends 
locating the connection at the remote location of the system - but this is by 
no means a requirement.

Placing the ITC a the end of the system will not guarantee removal of all air 
from the system. We specify an air bleed valve be located at the high point(s) 
of the system for that purpose.  I know there are automatic air releases that 
can be installed as well.

The problems associated with air in the system are valid; that's why a means 
should be provided to remove the air.  But excessive pressure from temperature 
rises is not one of those problems.  In fact, it is precisely because of 
trapped air that that most tree systems don't have excessive pressure problems. 
 The grids tend to have these issues because air can't be as readily trapped.  
That's why gridded systems should have a pressure relief. Of course, if you 
facilitate the removal of most air from a tree system, then a pressure relief 
is warranted on that system as well.

Locating the ITC at the riser will help reduce the amount of new air into the 
system, as well as reduce the amount of freshly oxygenated water as a result of 
testing.  This will reduce the potential for additional internal corrosion 
resulting from the oxygen in the system. (I seem to recall that this logic is 
used 'Down Under' as a means to extend the life of system piping)

So, given that the purpose of the ITC on a wet system is to test the flow 
alarm, it makes more sense to have it at the riser where it is more convenient 
to facilitate the testing. Removal of air should be completed by air bleed 
valves or automatic air releases.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104-7079

Direct:    701. 280.8591
Fax:        701.280.8739
Cell:        701.371.5759

[email protected]
www.ulteig.com

Confidentiality Notice
This message may contain privileged and confidential information. If you think, 
for any reason, this message may have been addressed to you in error, you   
must not disseminate copy or take any action in reliance on it, and we would 
ask you to notify me immediately by return email to [email protected].



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Medina Jr
Sent: Sunday, March 08, 2009 10:28 PM
To: [email protected]
Subject: Re: Test/Drain at the Riser

I?agree with you.


George Medina Jr.
Sr. Fire Sprinkler Designer
95-1015 Ka'apeha Pl.
Mililani, HI 96819
808-388-5974 CL#


-----Original Message-----
From: Byron Blake <[email protected]>
To: [email protected]
Sent: Sat, 7 Mar 2009 6:29 am
Subject: Test/Drain at the Riser


Here here. We witness the very same problem on large wet gridded systems, just 
as your experience and research indicates.?
?
We have one AHJ would REQUIRES test/drain ITCs. Guess where my false alarming 
issues are? I suspect this AHJ requirement is for their convenience and is not 
based on scientific laws of hydraulics and certainly not based on NFPA 
recommendations or typical trade practice. We have to live with the unintended 
consequences as a result of this "design compromise/requirement".?
?
Byron?
?
Byron Blake, CET?
Service/Inspections?
Freedom Fire Protection, LLC?
Longmont, CO?
?
-----Original Message-----?
From: [email protected]?
[mailto:[email protected]] On Behalf Of Rodney Hamm?
Sent: Sunday, March 01, 2009 5:38 PM?
To: [email protected]?
Subject: RE: statistics?
?
If anyone has any pull or influence with the development of NFPA 13........?
?
Please discuss the idiotic approach of installing Inspector's Test Connections 
at the sprinkler riser (~12 in. downstream of the flow switch).?
This has been considered "acceptable" by NFPA 13 since 2002 and is quickly 
becoming standard practice in the great state of Georgia. There are several 
significant reasons why this is a bad idea AND from an engineering standpoint 
this is a very poor design. The inevitable trapped air in the system causes or 
can potentially cause a number of problems: Excessive system pressure when 
temperatures increase, false water flow alarms due to air pocket 
expansion/contraction, failed water flow alarms due to cycling flow switches, 
increased rust on the interior surfaces of sprinkler piping, etc.?
?
>From what I have seen, most contractors or sprinkler designers who?
primarily?
install or design new systems have no idea this approach causes problems for 
the building owner and/or fire protection system inspectors. I can confirm 
these are common problems at several of the facilities I have visited over the 
past few years. In many instances, the only effective solution is to install a 
suitably located Inspector's Test Connection or bleed the air pockets using 
sprinklers at the highest elevations. We have installed air bleed off 
connections for numerous systems simply to allow trapped air to be removed from 
the high point. The problem is access at some facilities after the solid 
ceilings or other obstructions have been introduced.?
?
In my humble opinion, Inspector's Test Connections should be installed at the 
most remote point of each system. The connection point (prior to being piped to 
within 6 ft. of the floor level) should be at the highest elevation of the 
sprinkler system piping whenever possible. Auxiliary drains or low point drains 
should NOT be considered Inspector's Test Connections.?
?
I would assume it is safe to say anyone who has enough experience and personal 
dealings with inspections and/or problem solving (after the design phase and 
initial installation project has been completed) realizes that the Inspector's 
Test Connection serves more purposes than just testing the water flow alarms. 
{I have heard "the sole purpose of the ITC is to test the alarm device" so many 
times that I get a smile every time someone spouts it.} I simply disagree with 
the relatively recent change in NFPA 13 which allows this approach. I strongly 
believe the practice of installing the Inspector's Test Connection a few feet 
downstream of the water flow switch should be considered unacceptable.?
?
In many instances, the fire alarm companies and building owners have to deal 
with the issues caused by this poor design. They rarely if ever realize the 
true source or reason for the intermittent false alarms. They simple bypass the 
alarm or set the delays so high that flow switch cycling becomes a problem 
during alarm testing.?
?
We see systems with >175 psi on a regular basis caused by this 
problem.......some systems even peg the 300 psi gauges. On of my customers had 
5 separate incidents where sprinklers developed leaks and/or popped open due to 
excess system pressure during Spring & early Summer of 2007. We added pressure 
relief valves in August of 2007 for all of their wet systems and this resolved 
the problem. This is a >1 million sq. ft. facility with several wet systems. 
False fire alarms and excess air pressure are very common problems when the ITC 
is not located at the most remote and/or highest elevation of the system 
piping. I could provide many more examples, but I think I have made my point.?
?
Black steel, moisture and trapped air allows more rust to develop on the 
interior surfaces of the sprinkler piping than if the majority of the sprinkler 
piping is full of water. Therefore, it would be safe to conclude that trapped 
air in the sprinkler systems will shorten the life of the sprinkler system 
piping.?
?
The fact that someone or some group convinced the NFPA committee to change the 
standard and the fact that the approach saves time and money during 
installation does not make it a good engineering design!?
?
There are probably a few instances where placing the ITC a few feet downstream 
of the flow switch should be considered acceptable due to limited or no 
feasible alternatives; however, these instances should be the last resort 
alternative rather than standard practice.?
?
Just one man's perspective!! I wonder if anyone on this forum agrees with me on 
this subject.?
?
Rodney K. Hamm, P.E.?
President/Owner?
Falcon Fire Protection?
Office (478) 953-1677?
Cell (478) 396-6988?
?