Of course it is important to have the ITC at the furthest remote location for a 
dry system, since you do want to know the longest time it takes to get water on 
the fire, but as Ron pointed out, in a wet system the volumetric flow rates are 
the same, no matter where (elevation being equal) in the system that ITC is 
located.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



--- On Mon, 3/9/09, Timothy W Goins <[email protected]> wrote:

From: Timothy W Goins <[email protected]>
Subject: RE: Test/Drain at the Riser
To: [email protected]
Date: Monday, March 9, 2009, 10:34 AM

I respectfully disagree.

The purpose is to test the alarm device during a one head fire flow. Since
we have to time the device, putting it at the most remote area makes more
since, since we are simulating a fire at the most remote area and timing the
activation of the alarm device. The alarm device must activate before 90
seconds (Electric) and or 5 minutes (Water Motor Alarm) you pick.

If you are ONLY checking that the alarm device will work at the riser okay
then, but I don't believe that that is the intent of the ITC.

Just my opinion,

Timothy Goins

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Monday, March 09, 2009 8:44 AM
To: '[email protected]'
Subject: RE: Test/Drain at the Riser


Pardon me if this is ground that was already covered-

I specify the Inspector's test Connection to be located at the sprinkler
riser. This is NOT something that is new to NFPA-13 either.  E.g., the 1996
edition (4-15.4.2) does not require the location to be at the riser - it
doesn't specify any particular location. Commentary in the handbook that
year specifically states that the purpose of the connection is to "verify
the operation of the water flow alarm device(s)." The appendix dialogue
recommends locating the connection at the remote location of the system -
but this is by no means a requirement.

Placing the ITC a the end of the system will not guarantee removal of all
air from the system. We specify an air bleed valve be located at the high
point(s) of the system for that purpose.  I know there are automatic air
releases that can be installed as well.

The problems associated with air in the system are valid; that's why a
means
should be provided to remove the air.  But excessive pressure from
temperature rises is not one of those problems.  In fact, it is precisely
because of trapped air that that most tree systems don't have excessive
pressure problems.  The grids tend to have these issues because air can't
be
as readily trapped.  That's why gridded systems should have a pressure
relief. Of course, if you facilitate the removal of most air from a tree
system, then a pressure relief is warranted on that system as well.

Locating the ITC at the riser will help reduce the amount of new air into
the system, as well as reduce the amount of freshly oxygenated water as a
result of testing.  This will reduce the potential for additional internal
corrosion resulting from the oxygen in the system. (I seem to recall that
this logic is used 'Down Under' as a means to extend the life of system
piping)

So, given that the purpose of the ITC on a wet system is to test the flow
alarm, it makes more sense to have it at the riser where it is more
convenient to facilitate the testing. Removal of air should be completed by
air bleed valves or automatic air releases.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104-7079

Direct:    701. 280.8591
Fax:        701.280.8739
Cell:        701.371.5759

[email protected]
www.ulteig.com

Confidentiality Notice
This message may contain privileged and confidential information. If you
think, for any reason, this message may have been addressed to you in error,
you   must not disseminate copy or take any action in reliance on it, and we
would ask you to notify me immediately by return email to
[email protected].



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Medina
Jr
Sent: Sunday, March 08, 2009 10:28 PM
To: [email protected]
Subject: Re: Test/Drain at the Riser

I?agree with you.


George Medina Jr.
Sr. Fire Sprinkler Designer
95-1015 Ka'apeha Pl.
Mililani, HI 96819
808-388-5974 CL#


-----Original Message-----
From: Byron Blake <[email protected]>
To: [email protected]
Sent: Sat, 7 Mar 2009 6:29 am
Subject: Test/Drain at the Riser


Here here. We witness the very same problem on large wet gridded systems,
just as your experience and research indicates.? ? We have one AHJ would
REQUIRES test/drain ITCs. Guess where my false alarming issues are? I
suspect this AHJ requirement is for their convenience and is not based on
scientific laws of hydraulics and certainly not based on NFPA
recommendations or typical trade practice. We have to live with the
unintended consequences as a result of this "design
compromise/requirement".? ? Byron? ? Byron Blake, CET?
Service/Inspections?
Freedom Fire Protection, LLC? Longmont, CO? ? -----Original Message-----?
From: [email protected]?
[mailto:[email protected]] On Behalf Of Rodney Hamm?
Sent: Sunday, March 01, 2009 5:38 PM?
To: [email protected]?
Subject: RE: statistics?
?
If anyone has any pull or influence with the development of NFPA 13........?
? Please discuss the idiotic approach of installing Inspector's Test
Connections at the sprinkler riser (~12 in. downstream of the flow switch).?
This has been considered "acceptable" by NFPA 13 since 2002 and is
quickly
becoming standard practice in the great state of Georgia. There are several
significant reasons why this is a bad idea AND from an engineering
standpoint this is a very poor design. The inevitable trapped air in the
system causes or can potentially cause a number of problems: Excessive
system pressure when temperatures increase, false water flow alarms due to
air pocket expansion/contraction, failed water flow alarms due to cycling
flow switches, increased rust on the interior surfaces of sprinkler piping,
etc.? ?
>From what I have seen, most contractors or sprinkler designers who?
primarily?
install or design new systems have no idea this approach causes problems for
the building owner and/or fire protection system inspectors. I can confirm
these are common problems at several of the facilities I have visited over
the past few years. In many instances, the only effective solution is to
install a suitably located Inspector's Test Connection or bleed the air
pockets using sprinklers at the highest elevations. We have installed air
bleed off connections for numerous systems simply to allow trapped air to be
removed from the high point. The problem is access at some facilities after
the solid ceilings or other obstructions have been introduced.? ? In my
humble opinion, Inspector's Test Connections should be installed at the
most
remote point of each system. The connection point (prior to being piped to
within 6 ft. of the floor level) should be at the highest elevation of the
sprinkler system piping whenever possible. Auxiliary drains or low point
drains should NOT be considered Inspector's Test Connections.? ? I would
assume it is safe to say anyone who has enough experience and personal
dealings with inspections and/or problem solving (after the design phase and
initial installation project has been completed) realizes that the
Inspector's Test Connection serves more purposes than just testing the
water
flow alarms. {I have heard "the sole purpose of the ITC is to test the
alarm
device" so many times that I get a smile every time someone spouts it.} I
simply disagree with the relatively recent change in NFPA 13 which allows
this approach. I strongly believe the practice of installing the
Inspector's
Test Connection a few feet downstream of the water flow switch should be
considered unacceptable.? ? In many instances, the fire alarm companies and
building owners have to deal with the issues caused by this poor design.
They rarely if ever realize the true source or reason for the intermittent
false alarms. They simple bypass the alarm or set the delays so high that
flow switch cycling becomes a problem during alarm testing.? ? We see
systems with >175 psi on a regular basis caused by this problem.......some
systems even peg the 300 psi gauges. On of my customers had 5 separate
incidents where sprinklers developed leaks and/or popped open due to excess
system pressure during Spring & early Summer of 2007. We added pressure
relief valves in August of 2007 for all of their wet systems and this
resolved the problem. This is a >1 million sq. ft. facility with several wet
systems. False fire alarms and excess air pressure are very common problems
when the ITC is not located at the most remote and/or highest elevation of
the system piping. I could provide many more examples, but I think I have
made my point.? ? Black steel, moisture and trapped air allows more rust to
develop on the interior surfaces of the sprinkler piping than if the
majority of the sprinkler piping is full of water. Therefore, it would be
safe to conclude that trapped air in the sprinkler systems will shorten the
life of the sprinkler system piping.? ? The fact that someone or some group
convinced the NFPA committee to change the standard and the fact that the
approach saves time and money during installation does not make it a good
engineering design!? ? There are probably a few instances where placing the
ITC a few feet downstream of the flow switch should be considered acceptable
due to limited or no feasible alternatives; however, these instances should
be the last resort alternative rather than standard practice.? ? Just one
man's perspective!! I wonder if anyone on this forum agrees with me on this
subject.? ? Rodney K. Hamm, P.E.? President/Owner? Falcon Fire Protection?
Office (478) 953-1677? Cell (478) 396-6988? ?
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to