Careful on the IBC 509 provisions, i.e. so called "horizontal
firewalls". 

First and foremost anything horizontal isn't termed a wall. Second
firewalls must meet the criteria of being able to collapse on either
side, but not both, without effecting the opposite side. As Scotty once
said "Captain I cant defy the laws of physics !"  When the lower floor
goes, well I guess you know what happens next. So much for "horizontal
firewalls" and separate buildings created by them.

Lets take a closer look at 509, ....509.2 to be exact.  Heres what it
says; 

"A basement and/or the first story above grade plane of a building shall
be considered as a separate and distinct building for the purpose of
determining area limitations, continuity of fire walls, limitation of
number of stories and type of construction."

The commentary hits the nail on the head; "The subsections of Section
509 are EXCEPTIONS to the general HEIGHT AND AREA limitations of Chapter
5."  Nothing in there about exceptions for Chapter 9, Mixed Uses and
Sprinklers.  

 In the end its still a mixed use building where an allowance for
height, area and construction type has been made for a "3 Hr horizontal
assembly". Back in the day we called this taxpayer buildings making good
use of available land, parking below, commercial/mercantile at grade and
residential above the first floor. The IBC merely accomodates this with
regards to building construction.

So in the end if its mixed its 13.

Hope that helps

John Drucker
Fire Protection Subcode Official




 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jamie
Seidl
Sent: Friday, March 13, 2009 1:28 PM
To: [email protected]
Subject: RE: Mixed-Use Code Question

In IBC land, there is Separated and Non-separated mixed use. Non
separated, your entire building would be full 13.  In separated mixed
use, as long as the ratings meet the required separations or "separate
buildings" of the code, (including horizontal) you can use 13 for the
lower area and 13R for the upper.  There has been some contention on the
designation of a separate building and a horizontal fire barrier, but
this configuration has met the intent of the code in the jurisdictions
I've dealt with.
Jamie Seidl

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom
Duross
Sent: Friday, March 13, 2009 12:23 PM
To: [email protected]
Subject: Mixed-Use Code Question

I have a question about a small project I'm bidding and how it relates
to other's building codes.
Four storey 8 unit residential building, in bid stage, just got
notification that one unit, half the ground floor, will be zoned for
commercial use.
I'm at odds if this changes the building to mixed-use or not.  I've
asked the gc if he's still applying as an R2 and he's not sure,
architect in on vacation (go figure).  I'm leafing through our building
code (ICC-03) right now to see if this qualifies as ancillary with
regards to design (13 vs.
13R) but I just thought I'd ask the masses with a little time on their
hands how this would resolve under their current codes.  Often we have
similar provisions and interpretations and I don't have the workbook,
tabs or supplement yet for ours.  We're new to this edition.

I'm able to refer to 13 for design in areas like Basements but still
base the remainder of the system under 13R requirements and our old code
gave little guidance as to percentages with regards to areas outside of
the use group.  I'm wondering if, disregarding permit application for
now, the addition of one of the 8 units from residential use to
commercial use (will be a store) will effect the design.

Tom

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]