Here is a new one (to me) from our friends at the COE. Has anyone out
there run into this before and if so what did you do?

Unified Facilities Guide Specification, 3.4.6 Pipe Joints. "Grooved
joints shall ne be used in concealed locations, such as behind solid
walls or ceiling, unless an access panel is shown on the drawings for
servicing or adjusting the joint."

The drawings we have don't show and access panels in the gyp-board
ceilings so I guess we can't use grooved couplings.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024