Ron,

Here's what it says (see last sentence) and the Corps follows these
guidelines by law:

3.4.6 Pipe Joints
Pipe joints shall conform to NFPA 13, except as modified herein. Not more
than four threads shall show after joint is made up. Welded joints will be
permitted, only if welding operations are performed as required by NFPA 13
at the Contractor's fabrication shop, not at the project construction
site. Flanged joints shall be provided where indicated or required by
NFPA 13. Grooved pipe and fittings shall be prepared in accordance with
the manufacturer's latest published specification according to pipe
material, wall thickness and size. Grooved couplings, fittings and
grooving tools shall be products of the same manufacturer. For copper
tubing, pipe and groove dimensions shall comply with the tolerances
specified by the coupling manufacturer. The diameter of grooves made in
the field shall be measured using a "go/no-go" gauge, vernier or dial
caliper, narrow-land micrometer, or other method specifically approved by
the coupling manufacturer for the intended application. Groove width and
dimension of groove from end of pipe shall be measured and recorded for
each change in grooving tool setup to verify compliance with coupling
manufacturer's tolerances. Grooved joints shall not be used in concealed
locations, such as behind solid walls or ceilings, unless an access panel
is shown on the drawings for servicing or adjusting the joint.

On Thu, Apr 30, 2009 at 1:05 PM, Fletcher, Ron <[email protected]> wrote:
> Unified Facilities Guide Specification, 3.4.6 Pipe Joints



-- 
Ron Greenman
at home....