Also don't wrap the Protectowire around the sprinkler pipe. A fork 
lift can then take out both at once (It happened here in CT).


At 07:37 PM 5/4/2009, you wrote:
>Travis.
>
>Just thought I'd mention it as it was a train of thought mentioned to me;
>that there is a lot to be said for Double Interlock for larger freezer
>operations as if there is accidental discharge (fork list error) then the
>freezer has to be thawed out for clean up to take place. Stock can be
>wasted, store operations severely impacted...Just a consideration when doing
>your bean counting.
>
>I guess since I'm posting here I should take a minute to both introduce
>myself and thank the members of the forum. I've been receiving emails from
>the forum the last couple of weeks and am very impressed with the level of
>expertise on here. Was beginning to feel like a stalker:) but it seemed like
>all the posts were getting excellent replies so I figured I just sit on the
>side.
>
>Based in Chicago myself. See some familiar names from the AS forum.
>
>Damien Shannon.
>QED Sprinkler Designs, Inc.
>
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Travis Mack,
>SET
>Sent: Monday, May 04, 2009 12:58 PM
>To: [email protected]
>Subject: RE: Preaction: single vs double
>
>This one is multiple coolers / freezers.  -10F to 40F, depending on the
>area.
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Fletcher, Ron
>Sent: Monday, May 04, 2009 10:56 AM
>To: [email protected]
>Subject: RE: Preaction: single vs double
>
>Travis,
>
>Don't forget that a cooler doesn't need a dry system or even dry pendent
>sprinklers provided it doesn't freeze. The bigger the cooler the more stable
>the temperature.
>
>Ron Fletcher
>Aero Automatic Sprinkler
>Phoenix, AZ 85024
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Travis Mack,
>SET
>Sent: Monday, May 04, 2009 10:39 AM
>To: [email protected]
>Subject: RE: Preaction: single vs double
>
>Ok.  I think I found my answers already.  All preaction systems protecting
>storage can not be gridded.
>
>7.3.2.6 System Configuration. Preaction systems of the type described in
>7.3.2.1(3) and all preaction systems protecting storage occupancies,
>excluding miscellaneous storage, shall not be gridded.
>
>I can't find anything that limits my capacity.  So, the 750 gallon and 60
>second trips don't come into play, but I still have the 30% penalty and the
>limit to tree or looped.  Does this sound right?
>
>Thanks!
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Travis Mack,
>SET
>Sent: Monday, May 04, 2009 10:17 AM
>To: [email protected]
>Subject: Preaction: single vs double
>
>We have a cold storage warehouse where the owner wants a preaction system.
>The piping will run in a heated, combustible concealed space above the
>cooler/freezer.  The cooler will be supplied with dry pendent sprinklers.
>There is going to be a capacity issue with this system if it is double
>interlock.  If we go with single interlock, doesn't the capacity issue go
>away?  Because this is storage, I believe we will still need to have the 30%
>increase in design area, correct??  Also, can I grid a single interlock
>preaction system protecting a storage occupancy?
>
>Thanks in advance for your help.
>
>Travis
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>__________ NOD32 4052 (20090504) Information __________
>
>This message was checked by NOD32 antivirus system.
>http://www.eset.com
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>__________ NOD32 4052 (20090504) Information __________
>
>This message was checked by NOD32 antivirus system.
>http://www.eset.com
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to