bracing. i asked for bracing at endsand elbows of mains in the 12,000 sq. ft. design area. The bracing was only to be lateral bracing within 6 ft of these mentioned points. If this request is unreasonable and not-standard practice for a head replacement, then I will CHANGE my mind and the request.
I don't know if the sprinklers are different, but I bet they are. Outgoing sprinklers are from 1993 or so. That was another of my requests: that they provide the SIN for the sprinkler. The sprinkler contractor is a well known name. so they know how they want to play this game. Design includes minor density changes-- in some places up, in some places down, mostly the same. I am sure the area of coverage has changed, unless military did 3,000 square ft design areas back in the early 90's. they apparently were not E/Q bracing then. scot deal excelsior fire On Fri, May 8, 2009 at 9:53 PM, Scott A. Futrell <[email protected]> wrote: > Scot, > > I need more information about b. the bracing request. > > However, on a. IF they are changing one sprinkler for one sprinkler, with > the same density, k-factor, coverage and so on then I don't think all of > that detail is necessary. However, I completely agree and would say they > need to show enough of the existing sprinkler system to verify that the > changes are appropriate IF there is a reason to believe the original system > wasn't correct or appropriate, or IF walls are being removed and it was a > room design design before then they need to show piping, valve assembly, > underground and so on and provide calculations. IF they are changing the > area of coverage, it isn't one-for-one replacement, they are changing > k-factors, and so on then they need to show piping, valve assembly, > underground and so and provide calculations. > > There are several different scenarios that would have to be addressed > individually. > > Scott _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)