For those of you that don't do much Gov. / Military work, The UFC is the "Unified Facilities Criteria" (UFC 3-600-01) These projects have several FPE's involved. The Contracting/reviewing entity is often an FPE. The design entity is required to be an FPE. And the Contractors "Quality Control" is required to be an FPE.
So it sounds like Scott is the QCFPE for the contractor. This very much limits his scope to the contract documents and specific referenced documents. The original RFP and design criteria, are only of interest if the scope is not clearly defined by the construction documents. The for "Bid" and "For Construction" Doc's are what he must comply with. If the construction doc's say 3000SF design area, it is often a battle to try and get the reduction for QR allowed by 4.1. If the spec. clearly say's X+Y=Z then thats what you see if the contractor complied with. But is the spec. says "Determine" If X+Z=Y, you only have to report that info, not act on it. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman Sent: Monday, May 11, 2009 9:16 AM To: [email protected] Subject: Re: review of sprinkler plans ends up with GC requesting the reviewer to provide additional plan sheet because contractor don´t want to Guys, A few things from UFC 600-1 (2004 version but I think this is still the same in the current version) that Scot may be trying to comply with: 1-6: Requirements for FPEs: Projects involving fire rated construction, fire detection, fire suppression, or life safety systems require an FPE as an integral part of the design team. (FPEs input must not be limited to design analysis preparation or post-design review!) 4-2.3.4.1: Water Supply Adequacy Calculations: A Fire Protection Engineer (as defined in pph 1-6) must provide flow test data and calculations demonstrating adequacy of water supply for anticipated sprinkler system. Calculations must be submitted no later than 35% design submission. (For design/build projects, the adequacy of the water supply must be established during the RFP preparation phase. I can't get the table into the message so fyi the UFC requires 0.10gpm/3000 sqft for 60 minutes for light hazard. The table is at the below website: http://www.tpub.com/content/UFGScriteria/3_600_01/3_600_010037im.jpg And the exception: Where listed quick-response sprinklers are used throughout the system, the design area inTable 4-1 may be permitted to be reduced without revising the density as permitted in NFPA 13except for facilities that are required to comply with UFC 4-010-01, DoD Minimum AntiterrorismStandards for Buildings (although this may no longer be the case in the current version). The problem seems to (without the full document to peruse) squarely rests with the contract due to the crappy spec. To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)