Phil,

In the annex of the 2007 edition is something that might help:

A.8.5.4.1 Batt insulation creates an effective thermal barrier
and can be considered the ceiling/roof deck when determining
distances between deflector and ceiling. The insulation
needs to be installed in each pocket (not just above the sprinkler)
and attached to the ceiling/roof in such a manner that it
will not fall out during a fire prior to sprinkler activation

Based on this, if you had three inches of batt insulation, at
the top of the joist channel, it could be regarded as the
effective "deck" above the sprinkler deflector, which could
then be located 1" down from the bottom of the CWJ, and
remain 22" down from the face of the insulation.

Additionally, it's a possible solution would be to provide a layer
of non- or limited-combustible materials on the bottom of the
composite wood joists, forming a non-sprinklered combustible
concealed space above. The caveat there is that it forces the
remote area below to increase to 3,000 square feet.  You do
get to reduce the density, but you still have to calculate 3,000
square feet.

Those are some thoughts on what you can do. 

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website


Phil Nawrocki wrote:
>  Sirs,
>
> We have a contract to install fire sprinklers in a building with 24" deep
> TJI composite wood joist construction.  They are 24" on center.  I can find
> nothing in NFPA #13 deflector rules that allow the sprinkler deflector under
> obstructed construction to be below 22" from the deck.  Is there any other
> way to protect the area besides putting a sprinkler in each 24" wide joist
> space?
>
> Regards, 
>
> Phillip H. Nawrocki
> Design Manager 
> National Fire Sprinkler, Inc. 
> 1544 W. Grant St. 
> Phoenix, AZ 85007-3314 
> (602) 712-1180 Phone  Ext #33 
> (602) 712-1260 Fax 
> [email protected] 
> Fire Sprinklers Save Lives! 
>
>  
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>   
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to