So let's look at this logic stream.

If you had a 500 sf indoor storage area at say .30/3000sf adjacent to a 10,000 
sf office space .10/1500sf, different occupancies separated by appropriate 
rated assemblies, storage area constructed per code, would you extend the 
.30/3000 into 2500 sq. ft of the office space?

What if the office space was only 1500sf, then would you design the entire 
building, storage and office space at .30/entire area?   

I doubt any contractor would pay attention to a design criteria like that.

The design criteria should be appropriate for the space when appropriate 
physical separations between different occupancies are provided. I'm having a 
hard time finding any requirement in the IFC,IBC, NFPA or other reference to 
extend the higher design criteria into an adjacent space other than when they 
are open to each other.

There is wording in 13 that references the density for a particular occupancy 
hazard is to remain constant even if the design area is less than that 
indicated.  There are two methods of design mentioned, the density/area method 
or the room design method. 



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Sprinkler 
Academy - C Bilbo
Sent: Tuesday, June 02, 2009 1:27 PM
To: FORUM
Subject: IFC requirements


Hi Scott,
 
What a great reference for future use!  I can see where the 3,000 sq ft minimum 
could apply, but I don't really see how the IFC allows the reduction of the 
design to the room only (not that I thought it should).  Based on the language 
of 2704.5 which reads (and I realize you already know the language), "Indoor 
storage areas and storage buildings shall be equipped throughout with an 
approved automatic sprinkler system in accordance with Section 903.3.1.1. The 
design of the sprinkler system shall not be less than that required for 
Ordinary Hazard Group 2 with a minimum design area of 3,000 square feet (279 
m2). Where the materials or storage arrangement are required by other 
regulations to be provided with a higher level of sprinkler system protection, 
the higher level of sprinkler system protection shall be provided."
 
I would also read 2704.2.2.3 to base the design of the containment on the area 
of the room or of the storage here.  I don't think this is stating that the 
remote area for the sprinkler system could be reduced to that area. 
 
In this particular case, it's also my assertion that we would still look to 
NFPA 13 to find the direction for our minimum remote area size and which 
densities to apply when we have mixed occupancies. 
 
I think we are on the same page but wanted to run this by you to be sure.


It should be recognized that the above is my opinion as a member of the NFPA 13 
Committee on Installation Criteria representing the NFSA, and has not been 
processed as a formal interpretation in accordance with the NFPA Regulations 
Governing Committee Projects and should therefore not be considered, nor relied 
upon, as the official position of the NFSA nor the NFPA, nor any of their 
technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
845-878-4200 x138
www.sprinkleracademy.com
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to