Cecil,

Connecting the IFC and NFPA 13 dots is not always easy. Many design
professionals and code officials use Section 2704.2.2.3 to reduce the
design area because all H occupancies are prescribed by the IBC to have
a minimum one-hour fire barrier separating the Group H use from any
other mixed occupancies. I understand what the requirements of the IFC
hazardous materials sprinkler provisions are but realistically, NFPA 13
allows design areas to be adjusted using some form of fire-resistive
separation. The IBC prescribes the level of construction and degree of
fire-resistance and further prescribes the use of either listed
assemblies or fire-resistive construction designs validated by an ASTM
E-119 test. None of the codes and standards are perfect, but at least
the IBC does specify the use fire-resistive separation that has a
validated design.

The other reason is found in IBC Section 901.7. With the exception of
Group I, R and H-5 occupancies, automatic sprinkler protection is only
required in the Group H fire area, not the area of the building. If my
fire area is only 1,000 square feet, yet the IFC, NFPA 13, or any other
standard prescribes a larger design area, there is no real benefit in
increasing the design area. The IBC and IFC only anticipate a single
event: the fire occurs in the Group H and the automatic sprinklers
control the fire while the fire-resistive separation limits its spread,
or the fire occurs outside the Group H occupancy and the fire-resistive
construction limits the fire spread to the Group H. In the latter
scenario, the sprinklers will protect the stored hazardous materials if
the fire-resistive construction is compromised or has such a high heat
release and burning rates to exceed the design limits of the
fire-resistive assembly.

I will grant you I wish the language was improved and more explicit. But
as someone whose been dealing with hazardous materials for over 25 years
I can tell you these design approaches are commonly applied and are
approved by fire and building code officials.

Scott Stookey
Senior Technical Staff - Business & Product Development
International Code Council (ICC)
807 Sweetwater River Drive
Austin, Texas 78748-2238
Office: 1-888-422-7233 (ICC-SAFE) X 3473 (FIRE)
Cellular: 512-716-9595
[email protected]
www.iccsafe.org
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sprinkler
Academy - C Bilbo
Sent: Tuesday, June 02, 2009 12:27 PM
To: FORUM
Subject: IFC requirements


Hi Scott,
 
What a great reference for future use!  I can see where the 3,000 sq ft
minimum could apply, but I don't really see how the IFC allows the
reduction of the design to the room only (not that I thought it should).
Based on the language of 2704.5 which reads (and I realize you already
know the language), "Indoor storage areas and storage buildings shall be
equipped throughout with an approved automatic sprinkler system in
accordance with Section 903.3.1.1. The design of the sprinkler system
shall not be less than that required for Ordinary Hazard Group 2 with a
minimum design area of 3,000 square feet (279 m2). Where the materials
or storage arrangement are required by other regulations to be provided
with a higher level of sprinkler system protection, the higher level of
sprinkler system protection shall be provided."
 
I would also read 2704.2.2.3 to base the design of the containment on
the area of the room or of the storage here.  I don't think this is
stating that the remote area for the sprinkler system could be reduced
to that area. 
 
In this particular case, it's also my assertion that we would still look
to NFPA 13 to find the direction for our minimum remote area size and
which densities to apply when we have mixed occupancies. 
 
I think we are on the same page but wanted to run this by you to be
sure.


It should be recognized that the above is my opinion as a member of the
NFPA 13 Committee on Installation Criteria representing the NFSA, and
has not been processed as a formal interpretation in accordance with the
NFPA Regulations Governing Committee Projects and should therefore not
be considered, nor relied upon, as the official position of the NFSA nor
the NFPA, nor any of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
845-878-4200 x138
www.sprinkleracademy.com
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to