Frans,

Very curious to know how you got on with the Victaulic valve w/ 1300 gallons
to make the 60 sec requirement after making the adjustments discussed (or
anywhere close). I need to do a building with 8 dry systems (new
construction) that requires all the valves at a main header. The bulk main
to the actual area of protection for some of the systems is forcing capacity
well beyond 750 gallons (approx 900). The client originally was going with
Victaulic valves, based on the premise that the lower air pressure would
lead to less air to be exhausted prior to water being discharged. 
Trying to find out if there's a 'sweet spot' where the low air pressure
versus 'higher pressure' Dry Pipe valves work best.
Thank you for any insight you can provide.

Damien Shannon
QED Sprinkler Designs Inc.
(773) 704 2571
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Frans Stoop
Sent: Tuesday, April 28, 2009 8:25 PM
To: [email protected]
Subject: Slow responding dry pipe valves

Dear colleagues,

Our client has a rather large dry pipe system supplied by a Victaulic 
dry pipe valve complete with an accelerator.
The system responds to slow to the ITC: more than 3 minutes.
The contents of the system is approx. 1300 gallon.
The air pressure in the system was set lower (in compliance with the 
Victaulic installation sheets) than we are used to with dry pipe 
valves of other manufacturers.

The sprinkler contractor and the local Victaulic representative 
couldn't find the cause yet.
My personal impression is that the Victaulic mat take much more time 
between opening the test valve and water delivery than dry pipe 
valves of other brands.
Does anyone share this impression or had the same experience ? If you 
prefer, you may react off-forum.

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112  

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to