If it can hinder the discharge of a sprinkler due to it's location relative to 
the sprinkler and it's size, it's an obstruction.  

1) 6ft. sq platform; it's over 4ft, typically you'd put one under.  Used to be 
a rule of over 4ft in width or 10sq. ft., put a sprinkler below.

2) 10'x20' mezzanine; yes.

3) cat walk; that depends on how it's arranged based on width, relation of it 
in regards to position of sprinklers, so maybe or most likely.  But one would 
have to see the plans to make the final determination. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Keith Pepin
Sent: Tuesday, July 21, 2009 10:37 AM
To: [email protected]
Subject: open grate flooring

Can someone explain the intent of NFPA 13 2007 Sec 8.6.5.3.3 with regards to 
open grate flooring? I have 2 projects that are using this type of flooring in 
several different scenarios. 

1)       Open grate flooring platform 6ft sq, elevated 10 ft in a 25 ft bldg
for conveyor loading or servicing. Sprinklers below?

2)       Open grate flooring for a mezz 10ft W x 20ft L. Sprinklers below?

3)       Open grate flooring for a cat walk. Steel bldg 25H x 80L x 40W
sprinkler protection at the roof level. Cat walk 6ft below roof and take up 
half the bldg. Used for light suspension below that can be moved around.
(Event center)

 

Thanks in advance.

Keith

 

 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to