Everything both of you are saying is understandable and applicable, Just
picture this; 2 layer system with 6 foot vertical separation w/ open floor
grating 75% plus open. Just does seem that was the intent. Perhaps AHJ
should be consulted? 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, July 21, 2009 11:44 AM
To: [email protected]
Subject: RE: open grate flooring

As for skipping, you'd be required to use intermediate level sprinklers, or
head guards with umbrellas. Prevents cold-soldering from roof sprinklers.

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Tuesday, July 21, 2009 11:33 AM
To: [email protected]
Subject: RE: open grate flooring

If you read the handbook it says pretty much what G said about storage dust
mats, and as far as the "Cat Walk" goes, I'd say the structural members that
are supporting the cat walk, Mezz. and landing will also work to obstruct or
deflect the sprinkler spray.

As far a skipping and over discharge, it would be no worse than if these
were 4+' wide ducts. The committee must think that this is acceptable, since
they haven't required that these heads be added to the hydraulic design for
all the years this has been in the standard. Roland? Anyone on committee to
comment?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


The 3rd scenario would require 2 layers of sprinkler near the ceiling for
half the building footprint. I have concerns what it would do to actual
sprinkler activation, skipping, over discharge...etc

Subject: RE: open grate flooring

If it helps you internalize it, picture some storage atop the catwalk or
mezz as an obstruction to spray; or a floor mat of some sort acting as a
dirt/duct barrier also blocking spray. You don't see em now, but they appear
later in occupancy phase.

glc


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to