Geoff:

Unless those fire retardant-sprayed areas are somehow isolated from the 
remainder of the attic, it would seem you would have to include them in your 
area (2 systems).  BTW - are you confident you can meet the volume and/or trip 
time requirements with just one system?

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Geoff Dyce
Sent: Wednesday, August 12, 2009 9:20 AM
To: [email protected]
Subject: attic

We have an attic that is 53,000 sq ft.  3000 sq ft has been sprayed with
fire retardant. (dormers and eves)  Can we say we have 50,000 sq ft or is
the area still considered 53,000 sq ft??  2 dry systems vs 1 dry system??



Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Veteran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  [email protected]