I think that 8.9.5.3.2 would pretty much allow you to use the ECSW heads
under OH doors, though.

On Tue, Sep 15, 2009 at 12:50 PM, Ed Kramer <[email protected]> wrote:

> Section 8.4.3 states "Extended coverage sprinklers shall only be installed
> as follows:".  The 4 items that follow it don't include OH doors.  Am I
> being too literal (again!)?
>
> Ed Kramer
> Littleton, CO
>
> > -----Original Message-----
> > From: [email protected] [mailto:sprinklerforum-
> > [email protected]] On Behalf Of Ben Young
> > Sent: Tuesday, September 15, 2009 10:46 AM
> > To: [email protected]
> > Subject: Re: sidewall sprinks under OH doors
> >
> > Why not?  I installed Tyco ECOH heads in a fire station in Myrtle Beach,
> > and
> > there were no issues with them.  There's nothing in the listing the
> > specifically excludes them from that use.
> >
> > On Tue, Sep 15, 2009 at 12:40 PM, Ed Kramer <[email protected]> wrote:
> >
> > > I need a reality check:  Section 8.4.2 (07) addresses sidewall
> > sprinklers
> > > and states sidewall sprinks can be installed to protect areas beneath
> > OH
> > > doors.
> > >
> > >
> > >
> > > Section 8.4.3 addresses extended coverage sprinklers and doesn't
> > mention OH
> > > doors.
> > >
> > >
> > >
> > > I interpret the above to mean that standard coverage sidewall sprinks
> > can
> > > be
> > > installed beneath OH doors, but extended coverage sidewall sprinks
> > can't.
> > > Correct?
> > >
> > >
> > >
> > > Ed Kramer
> > >
> > > Littleton, CO
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > For Technical Assistance, send an email to: [email protected]
> > >
> > > To Unsubscribe, send an email to:Sprinklerforum-
> > [email protected]<to%[email protected]<to%[email protected]>
> >
> > > (Put the word unsubscribe in the subject field)
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> > [email protected]
> > (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to