Thinking in terms of cross connection, though, I think I would shut down the sprinkler system, crack the drain, and see if there is flow. Then I would throttle the domestic, keeping some flow to push water toward the sprinklers. then, with a stethoscope or one of those fancy gadgets I'd try to pinpoint where there is flow. Larger pipe towards smaller, of course.
On Thu, Sep 24, 2009 at 5:07 PM, ParsleyConsulting < [email protected]> wrote: > I'm with you on this one Ed. I'm wondering if someplace in that > building someone hasn't made a cross connection to the domestic system? > -- > PARSLEY CONSULTING > Ken Wagoner, SET > 760.745.6181 voice > 760.745.0537 fax > [email protected] <mailto:[email protected]> e-mail > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website > > > Ed Vining wrote: > > How about starting by shutting off the domestic supply? A well maybe? If > > that doesn't start you towards it, you may have found the fountain of > > youth. > > > > Ed Vining > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > -- Ed Vining 4819 John Muir Rd Martinez CA 94553 925-228-8792 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)