One of my projects today is to get him the sections of 20 on settings 
and 25 on maintenance and testing. I'm doing a full test with the ITM 
contractor next week and hopefully we will re-set the pressures.


At 07:35 AM 10/28/2009, you wrote:
>For obvious reasons the system appears to be under unnecessary surges and
>stresses.  Did you advise the JP be set per #20?  Hopefully it's not
>'another' installation where the JP doesn't match the FP.
>TD
>
>
>I was at a location yesterday where they have had a problem of splits
>in CPVC pipe in a basement. The fire pump churn is roughly 175 psi
>but the jockey pump is set at 150 psi. Would repeated water hammer
>from weekly/quarterly/annual tests create enough fatigue to cause failure?
>