The use of the 20 to 30 pounds of air is to look for "gross leaks" like
a joint that wasn't glued, etc.  If the pressure does not hold at all
then you can walk the system and find the offending fitting.   Much
better than finding the same gross leak with water pouring out of a
fitting and potentially damaging things under it, especially a refit job
in or above a finished space. 


Kevin Law, PE
Bechtel National, Inc.
Waste Treatment Project
Fire Protection Engineering
Work  (509) 371-3280
Cell    (509) 531-5715


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Wednesday, October 28, 2009 7:52 AM
To: [email protected]
Subject: RE: Homeowner needs advice

I don't know what they have so can't comment specifically.  

>From the do's and don'ts from Blazemaster:

In bold face - WARNING: AIR OR COMPRESSED GAS MUST NEVER BE USED FOR
PRESSURE TESTING 

And normal text -

Fill lines slowly and bleed the air from the system prior to pressure
testing.  

And -

After cut-in cure times are met, the system must be slowly filled with
water and the air bled from the furthest and highest sprinkler heads
before test pressure is applied (refer to manufacturer's installation
instructions regarding Hydrostatic Testing). 

And -

After cut-in cure times are met and the air is bled from the system, it
is recommended that portion of the sprinkler system containing the
cut-in tee be pressure tested. Prior to pressure testing, the system
must be sectioned off to its smallest area using floor valves, etc., to
isolate the cut-in area. It is further recommended that the test
pressure applied should not exceed 50 psi over the system pressure. This
approach will minimize the potential for water damage should a leak
occur.

That's rather clear to me TESTING!  I don't see anything related to
normal return to service after whatever.  13 would not normally require
a new test for some add and relocates as I'm guessing was the scope of
work.  So not testing would be code compliant in this case.  Again I
would bet fitters in the field rarely if ever bleed the air for testing
on new systems.  Wrong?
Technically.  Sure they don't fill and pressurize with air they know to
use water.  Although I do know some fitters will put 20-30psi of air on
the
system to make sure it's holding before they fill with water.   Of
course I
asked what good knowing it was leaking did them if they couldn't see air
leaks and most likely could hear them either.  Yeah, well ummmmmm.....ya
see....  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: Bill Brooks [mailto:[email protected]]
Sent: Wednesday, October 28, 2009 8:32 AM
To: [email protected]
Subject: RE: Homeowner needs advice

Chris,

I like your response but could you discuss (via the forum) the product
spec sheet issue raised by the homeowner.  If removing the air doesn't
matter, why does the spec sheet highlight it?  Is this only applicable
to the initial hydrostatic test?  I think this would close the loop for
the homeowner.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Wednesday, October 28, 2009 9:21 AM
To: [email protected]
Subject: RE: Homeowner needs advice

I think Ed confused the issue.  He's not wrong but I don't see it as
applicable.  Hydrostatic testing is not the question.  The bleeding of
air for test purposes is recommended because yes it will create a
serious hazard if it ruptures.  I'd venture though this bleeding is not
actually done in the field. This testing is done at 200 psi.  Your
system most likely does not have this kind of pressure on it.  And even
if it did most of what is in
the system is water not air.   

Air is compressible, water is not for these purposes. This is why air at
pressure is dangerous and water not as much.  The volume of the air is
also a critical factor.  A little air at very high pressure is not as
big an issue as a lot of air at a lower pressure.  Think when air is
compressed energy is retained.  The more volume of air, the higher the
pressure the more retained energy.  When the pipe breaks this energy is
released.  The
water not being compressible does not retain as much energy.    

There is no reason really to bleed the air in the situation described.
Actually some air in the system is a good thing.  Because it is
compressible is "absorbs" temperature changes and pressure surges much,
much better than water.  Think of it like a spring.  If there was no air
in the system and the temperature rose just a few degrees the pipe would
break.  This is the ratio of Pressure = Temperature from basic science.

Taking an empty system at 0 pressure and filling it with water at street
pressure leaves the air in the system, true.  But after it's compressed
to street pressure (much <200 psi, probably in the 80 range) there is
very little volume left.  Recall the ratio of Pressure * Volume = a
steady value with no changes to Temperature from basic science.  Double
the pressure =
1/2 the volume.  With average street pressure you are doubling the
pressure many, many times.

If one suspects trapped air is causing false alarms like George
suggested the real problem is a leaking check valve.  Each time the
system surges from the city supply the new high pressure should be
locked in.  This could take a couple hours to a couple days to stabilize
at the highest pressure.  But at least in these parts surges in the
street are not that common on scale or duration to cause false alarms.  
 
Again there is no reason to bleed the air in your situation.
  
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, October 27, 2009 6:41 PM
To: [email protected]
Subject: Homeowner needs advice

I'm not sure how this email forum works.  I'm sending this out blind
hoping one of you pros has some advice for me.

I am a homeowner in a three-story townhouse.  Recently, a company did
some minor modification to our fire sprinkler system - moving a couple
of heads for a basement remodel.  When they were done with the pipe and
heads, they simply re-pressurized the system without bleeding out the
air trapped in the lines.  From what little I know about it, I thought
this step was very important to eliminate any pressurize air in the
system and preventing dangerous surge pressures.  It says so in big bold
type on the product spec sheet for the CPVC pipe.  When I asked the
installer he said they don't need to bleed it, but couldn't explain why
not.

Before I go raising a stink about it, I want to know if your forum
agrees that it's not necessary; or do I need to pester them into doing
it correctly.

Thanks.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to