We are reviewing a proposal to install sound baffles suspended from the roof, 
and evaluating obstructions to sprinkler discharge.   The baffles are 2 ft. 
deep panels hung vertically every ft.  The top of the baffle is just over 18 
ins. From the sprinkler heads so NFPA 13 would indicate that there is no 
obstruction problem because they do not exceed the 4 ft. obstruction trigger 
for obstruction more than 18 in. below the heads. 

However, the panels are every foot and it sure seems like a significant 
obstruction, but the installation does not violate NFPA 13 for obstructions.

Has anyone ever dealt with this issue and offer any insight.

Thanks,

Rich Richardson
Seattle Fire Department