The difference between a 5.6K orifice and a 5.62K is only .20 GPM @ 100 PSI,
so unless your calculating discharge at very high pressures who cares.
Conversely at 1PSI the difference is only .01 GPM. See we start using
computers that carry every calculation to 3 decimal places and that is the
level of accuracy we expect, until you realize we started with a lot of
assumptions, multiplied those by fluffy calculations, and then applied an
accuracy of .001?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, November 05, 2009 12:49 PM
To: [email protected]
Subject: Re: 5.62 K Factor

If you're "proving" this pipe schedule system to current standards then you
would use the nominal 5.6 that all 5.6 range heads use now.
The real question though, as someone mentioned yesterday, is why are you
being required to "prove" a pipe schedule system?

On Thu, Nov 5, 2009 at 11:21 AM, George Medina <[email protected]> wrote:
> I thought reliable F1FR were 5.62 but checked there data sheet and 
> noticed 5.6. I was told that a project had 5.62 heads that I had to 
> make a proof calc for but now the plan checker wants to know the make 
> and model.
>
> George Medina Jr
> Sr. Fire Sprinkler Designer
> 808-351-3987
>
> On Nov 4, 2009, at 7:34 PM, "Thomas Watt" <[email protected]> wrote:
>
>> All makes, many models. Are you trying to identify a sprinkler?
>>
>>
>> ----- Original Message -----
>> From: <[email protected]>
>> To: <[email protected]>
>> Cc: <[email protected]>
>> Sent: Wednesday, November 04, 2009 10:17 PM
>> Subject: 5.62 K Factor
>>
>>
>>> Anybody know the make and model of a sprinkler head with a 5.62 k? 
>>> of hand?
>>>
>>> Thanks Guys,
>>> George Medina
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: 
>>> [email protected]
>>>
>>> To Unsubscribe, send an email to:Sprinklerforum- 
>>> [email protected] (Put the word unsubscribe in the subject 
>>> field)
>>
>>
>> ---
>> ---
>> ---
>> ---
>> --------------------------------------------------------------------
>>
>>
>>
>> Internal Virus Database is out of date.
>> Checked by AVG - www.avg.com
>> Version: 8.5.374 / Virus Database: 270.12.69/2176 - Release Date:
>> 06/14/09
>> 17:54:00
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [email protected] (Put the word unsubscribe in the subject 
>> field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to