Actually I said there has been no not one case of cutting oil problem.  

Top Myers
RelMark Group
961 Pottstown Pike
Chester Springs, PA 19425
Office 610-321-2415   Cell 610-952-0965
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Craig
Leadbetter
Sent: Friday, November 06, 2009 7:46 AM
To: [email protected]
Subject: RE: Incompatible products with CPVC 

I find it interesting that you state that the manufacturers have only
found one loss due to cutting oil. 

We had a project where there were several piece of pipe that started to
leak. When the faulty pipe was taken out of the system there were
visible cracks, these cracks were not near the end of a pipe where
cutting had taken place. 

We sent samples to the factory and they reported that they believe the
fractures were caused by cutting oil weakening the product. 

I am sure am not the only contractor that has been given that report. Is
it possible that because they are the manufacturer that they get to
waive their magic wand and it is always something that the contractor
did and never an issue with their product?

We continue to install CPVC piping and have become very aware of the
compatibility issues and the need to check the compatibility listings on
the manufacturer's web sites. The compatibility list is an ever evolving
document and frequent review of the site is recommended. 

 

Craig Leadbetter
Safeguard of Marquette
(P)906-475-9955 Ext 101
(F) 906-475-5474
(C) 906-362-5393


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Top Myers
Sent: Thursday, November 05, 2009 7:00 PM
To: [email protected]
Subject: RE: Incompatible products with CPVC 

Having read this string of emails it is like the story of the eight
blind me describing an elephant.  We all know what we know and feel but
only have some of the picture and my biggest single complaint with CPVC
is all the manufacturers have enjoyed cashing the checks of contractors
who buy their product but have not been there to help with many of the
problems, have not educated the general contractors, design
professionals and AHJ's as to how to properly install CPVC and avoid
issues.  As a result we are seeing more and more contractors and
property owners quietly using alternative products.  This is unfortunate
as CPVC is a great product which deserves better more realistic honest
marketing. Some simple facts:  

- CPVC problems are not only one manufacturer
- I have discussed with all major manufacturers and they have not been
able to identify one job where problems came from cutting oil
- Some of biggest losses involve fire stop listed for use with CPVC by
UL but on Lubrizol incompatible list
- Extra stress by hangers UL listed has contributed to losses
- put light coating of solvent on fitting and more on pipe and you will
not have paddling inside pipe which can cause cracks
- Cat 5 wire can cause problems laying on CPVC.  Solution is to keep
wire off pipe and make sure everyone knows this

CPVC can be installed without problems and our industry needs it. We
need help and less marketing from the manufacturers and Lubrizol. 

Top Myers
RelMark Group
961 Pottstown Pike
Chester Springs, PA 19425
Office 610-321-2415   Cell 610-952-0965
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd -
FPDC
Sent: Tuesday, November 03, 2009 8:00 PM
To: [email protected]
Subject: Re: Incompatible products with CPVC 

The issue seems to be more when used with steel as opposed to on it's  
own.

Sent from my iPhone

On Nov 3, 2009, at 7:36 PM, "Terri Leyton"  
<[email protected]> wrote:

> When will someone challenge the listing of the product?  Whose  
> problem is it, if the product is properly approved and listed for  
> use by "approving agencies"?
>
> Just asking the question out loud.  No opinion or advice being given.
> T
>
> Terri Simmons Leyton
> PROTECTION DESIGN & CONSULTING
> Ph:      858-751-2930 - ext. 101
> Fax:    858-751-2933
> Cell:  619-871-8450
>
> Show class, have pride, and display character. If you do, winning  
> takes care of itself. --Paul Bear Bryant
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to