Realize that "Seismic separations" and expansion joints are not the same.
Seismic separations act like two independent structures and can move
independent of each other in a seismic event. (Hence the elaborate swing
joint or flex assembly requirement.)

An expansion joint is simply a weak point in a structure that MAY move
differentially in a seismic event. (Only requires a (single)flex coupling
within 24" of the joint, when located in a seismic zone facility.)

If your structure does not require seismic protection at all, the flex
couplings are not required by 13 because their use is only directed by 9.3,
just like you don't install a flex coupling at the base of the riser when
you're not required to for seismic.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Hinson, Ryan
Sent: Thursday, November 19, 2009 10:28 AM
To: [email protected]
Subject: RE: expansion joints

See NFPA 13(2007) section 9.3.2.3*, 9.3.2.4*, and 9.3.4* for seismic
flexible coupling requirements.  Building codes may have some additional
direction.  Per NFPA it looks like they are only required in seismically
sensitive areas.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, November 19, 2009 11:10 AM
To: [email protected]
Subject: expansion joints

I was under the impression that flexible couplings had to be installed
within 2 ft of an expansion joint in a building. I can't find any reference.
Am I making stuff up again?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to