Well anyone (almost) can answer the actual question.  Has anyone else  
run into issues with location of the seismic separation assembly?

Roland

On Nov 23, 2009, at 1:11 PM, Thom McMahon wrote:

> 9.3.2.3 Systems having more flexible couplings than required
> by this section shall be provided with additional sway bracing
> as required in 9.3.5.3.7. The flexible couplings shall be installed
> as follows:
> (4)*Within 24 in. (610 mm) of building expansion joints
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland
> Huggins
> Sent: Monday, November 23, 2009 1:42 PM
> To: [email protected]
> Subject: Re: expansion joints
>
> The standard does not say explicitly where to install the fitting at
> an seismic separation assembly.  I understand there is a cut-sheet out
> there that says having a flange within 2 ft of the wall assembly is
> adequate.  This means that you can have a single piece of pipe
> penetrating both wall assemblies that are designed to move
> differentially.   From my way of thinking, you have to have the device
> within the plane of the two wall assembly to avoid undo stress on the
> one stick of pipe.  We intend to attempt to clean this up next cycle.
>
> Was out last week so pardon the delayed response.
>
> Roland
>
>
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to