Well anyone (almost) can answer the actual question. Has anyone else run into issues with location of the seismic separation assembly?
Roland On Nov 23, 2009, at 1:11 PM, Thom McMahon wrote: > 9.3.2.3 Systems having more flexible couplings than required > by this section shall be provided with additional sway bracing > as required in 9.3.5.3.7. The flexible couplings shall be installed > as follows: > (4)*Within 24 in. (610 mm) of building expansion joints > > Thom McMahon, SET > Firetech, Inc. > 2560 Copper Ridge Dr > P.O. Box 882136 > Steamboat Springs, CO 80488 > Tel: 970-879-7952 > Fax: 970-879-7926 > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Roland > Huggins > Sent: Monday, November 23, 2009 1:42 PM > To: [email protected] > Subject: Re: expansion joints > > The standard does not say explicitly where to install the fitting at > an seismic separation assembly. I understand there is a cut-sheet out > there that says having a flange within 2 ft of the wall assembly is > adequate. This means that you can have a single piece of pipe > penetrating both wall assemblies that are designed to move > differentially. From my way of thinking, you have to have the device > within the plane of the two wall assembly to avoid undo stress on the > one stick of pipe. We intend to attempt to clean this up next cycle. > > Was out last week so pardon the delayed response. > > Roland > > > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)