A recent annual sprinkler inspection found several head guards damaged and in 
need of replacement.
NFPA 2002 13-6.2.8 states: "Sprinklers subject to mechanical injury shall be 
protected with listed guards."
NFPA 1996 13-2.1.1 states: "all materials essential to successful system 
operation shall be listed." This system was installed around 1994-1996.
 
The sprinkler heads are Central Model A. I contacted Tyco Tech support and they 
told me they no longer manufacture or have remaining stock of head guards for 
this sprinkler.
Tyco checked to see if the current Tyco heads replaced the Model A, but they 
did not. So, there is no listed head guard available.
Also, I am not certain if the installing contractor even used the Central head 
guard. I am trying to get a data sheet from Tyco to determine if the correct 
head guard was used.

Question 1:
If there are no head guards available, the owner must change the sprinkler to a 
newer model with a head guard available, right?
Question 2:
If it is determined the installing contractor did not use the listed head guard 
and a generic brand was approved by the AHJ at time of installation, could we 
replace with the same generic brand (if it is available)? This is be contrary 
to NFPA 13.




Forest Wilson 

Project Manager 
Cherokee Fire Protection Co. 
1855 Bellbrook Ave. Ste C
Xenia OH 45385

ph: 937-376-2333 
fx: 614-455-4324 
cell: 937-307-5647 


. 



Visit our blog: www.cherokee-fire.blogspot.com 







NOTICE: The information contained in this email is intended to be solely for 
the use of the named individual or entity to which it is directed and may 
contain information that is privileged or otherwise confidential. It is not 
intended for transmission to, or receipt by, anyone other than the named 
addressee (or a person authorized to deliver it to the named addressee). It 
should not be copied or forwarded to any unauthorized persons. If you have 
received this electronic mail transmission in error, please delete it from your 
system without copying or forwarding it, and notify the sender of the error by 
reply email or by calling Cherokee Fire Protection Co. at 888-347-3079 toll 
free.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to