A recent annual sprinkler inspection found several head guards damaged and in need of replacement. NFPA 2002 13-6.2.8 states: "Sprinklers subject to mechanical injury shall be protected with listed guards." NFPA 1996 13-2.1.1 states: "all materials essential to successful system operation shall be listed." This system was installed around 1994-1996. The sprinkler heads are Central Model A. I contacted Tyco Tech support and they told me they no longer manufacture or have remaining stock of head guards for this sprinkler. Tyco checked to see if the current Tyco heads replaced the Model A, but they did not. So, there is no listed head guard available. Also, I am not certain if the installing contractor even used the Central head guard. I am trying to get a data sheet from Tyco to determine if the correct head guard was used.
Question 1: If there are no head guards available, the owner must change the sprinkler to a newer model with a head guard available, right? Question 2: If it is determined the installing contractor did not use the listed head guard and a generic brand was approved by the AHJ at time of installation, could we replace with the same generic brand (if it is available)? This is be contrary to NFPA 13. Forest Wilson Project Manager Cherokee Fire Protection Co. 1855 Bellbrook Ave. Ste C Xenia OH 45385 ph: 937-376-2333 fx: 614-455-4324 cell: 937-307-5647 . Visit our blog: www.cherokee-fire.blogspot.com NOTICE: The information contained in this email is intended to be solely for the use of the named individual or entity to which it is directed and may contain information that is privileged or otherwise confidential. It is not intended for transmission to, or receipt by, anyone other than the named addressee (or a person authorized to deliver it to the named addressee). It should not be copied or forwarded to any unauthorized persons. If you have received this electronic mail transmission in error, please delete it from your system without copying or forwarding it, and notify the sender of the error by reply email or by calling Cherokee Fire Protection Co. at 888-347-3079 toll free. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)