In the past when we have run across this, we have been required to put
sprinklers in the concealed space.  The only thing you could reference is:

A.8.15.1.2.1  Minor quantities of combustible materials such as but not
limited to: cabling, nonmetallic plumbing piping, non-structural wood, etc.
can be present in concealed spaces constructed of limited or noncombustible
materials but should not typically be viewed as requiring sprinklers (see
8.15.1.1). For example, it is not the intent of this section to require
sprinklers, which would not otherwise be required, in the interstitial space
of a typical office building solely due to the presence of the usual amount
of cabling within the space.  The threshold value at which sprinklers become
necessary in the concealed space is not defined.

I am assuming the ceiling is non-structural wood, but I don't know what
defines a 'minor quantity.'  I would further assume that a minor quantity is
what some lawyer wants it defined as when you are on the witness stand
defending why you didn't put sprinklers in the 'obviously' combustible
concealed space. (stated in my best Perry Mason - like accent)

Merry Christmas to all!

Travis

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jimmy Waite
Sent: Tuesday, December 15, 2009 11:53 AM
To: AFSA Sprinkler Forum
Subject: Drop Wood Ceiling

Gentlemen,

 

We have a situation where an engineer in requiring sprinkler protection
above a drop wood ceiling.  The building is light hazard and noncombustible,
and we have obviously provided protection below the ceiling.  I can't place
a code reference in defense of either side.  It would seem that we have
adequately protected the wood ceiling by protecting the floor space below
it.  On the other hand, the back of the wood ceiling would mean there are
combustibles in a concealed space.  What is everyone's opinion?

 

Thanks,

 

Jimmy Waite

Design Engineer


Piedmont Fire Protection Systems, LLC                            

3609 Bastion Lane            

Raleigh, NC  27604


o: 919.212.2356  

f:  919.212.2357  

 <mailto:[email protected]> [email protected]

web:  <http://www.piedmontfire.com/> www.piedmontfire.com


 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

__________ NOD32 4690 (20091215) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to