I spoke with Greg and he is clear as mud now.

Merry Christmas!

Travis
> I am assuming you are talking a light hazard small room that meets the
> requirements of a small room.  In small rooms, you take the area of the
> room divided by number of heads.  That is how I was taught.  You would
> require 4 heads in this room as a minimum.  It is 742.5 sq ft.  742.5 / 3
> = 247.5.  So, you are going to need to space so that you are 9' from the
> wall in the 16'-6" dimension, but you will need to be 11.25' on center in
> the 45' dimension if equally spaced.
>
> 8.6.2.1.2  The requirements of 8.6.2.1.1 shall not apply in a small room
> as defined in 3.3.15; the protection area of coverage for each sprinkler
> in the small room shall be the area of the room divided by the number of
> sprinklers in the room.
>
>
>> Hello and Merry Christmas,
>>
>> Maybe I am tired or something, but I am more confused now than before
>> for rooms with multiple heads in them.
>>
>> If you have a rectangular room 16-6 wide and 45 feet long... You are
>> spaced 7-6 to head and 9-0 to opposite wall in the narrow dimension;
>> what is the maximum spacing between the heads going the length of the
>> room.
>> And due to lights the spacing will be greater than 45' divided by 4
>> heads.
>>
>> Thanks,
>>
>> Greg McGahan
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
> --
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>


-- 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to