LOL, Good luck changing the mind of an EOR even with irrefutable proof.
After I passed the test my wife got me a sign "Never, but never question the
judgment of the ENGINEER".  (I hang it proudly but certainly accept
questioning). 

I assume you asked for chapter and verse of the NEC EOR is referencing.

If you follow this forum regularly you will find a big theme is EOR's and
AHJ's making stuff up that is not in Code.  And in most cases we contractors
lose.  

Did you call NFPA?  Those folks are great.  I'd start with the NEC guys
because it's really their issue, not a sprinkler issue.  If you search the
archives I believe John Drucker did a thorough job on the matter some time
ago.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eladio N.
Alvarado
Sent: Monday, January 04, 2010 10:38 AM
To: [email protected]
Subject: RE: Electrical Rooms

Eric:

I understand and agree with you, but the EOR insist that the 4" main to the
FD Connection, which by the way is dry (check valve in another space) should
not cross the room since is in violation of NEC, according to their
interpretation. I have already recited chapter and verse of the code
requirements and exceptions, but it doesn't seem to sink in. There may other
issues that affect their perception or attitude, but I'm kind stuck, and
would really like to find irrefutable proof to my point.

Eladio Alvarado
AFSDII

-----Original Message-----
From: [email protected]
[mailto:[email protected]]on Behalf Of Eric Tysinger
Sent: Monday, January 04, 2010 10:37 AM
To: [email protected]
Subject: RE: Electrical Rooms

To my knowledge, there is nothing from NFPA 13 that addresses this. The
clearance requirements are found in the NEC, and there is nothing in the NEC
that prohibits piping from entering and exiting the electrical room. Don't
forget there are rules in NFPA 13 that allow the sprinkler to be omitted. I
try to use these to avoid the questions all together.

Thanks,
Eric Tysinger CET
NICET 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032
f: (704)795-6838
C: (239)633-9703


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eladio N.
Alvarado
Sent: Monday, January 04, 2010 9:31 AM
To: [email protected]
Subject: Electrical Rooms

Happy New Year to all!!

I know that we have previously discussed Electrical Equipment rooms, and
that the general consensus is that there is nothing in NFPA 13 that
prohibits sprinkler pipe, be it mains and/or branch lines from entering the
room, as long as it doesn't violate the require perimeter area of the
particular equipment. Now my question is; is there a technical
interpretation from NFPA 13 that explains this, and that someone in the
forum may be aware of? I could really use this info to nail this subject
closed with the EOR.

Thanks in advanced,

Eladio Alvarado
AFSDII


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to