Remember that the Architect may not want to use the exception for 13R or 13D in I-1 if he needs to retain the "fully sprinklered per NFPA 13" status that he made need for many IBC code exceptions/modifications such as the allowable building area increase [506.3], rating reductions [508.3.3, Table 601, 708.3], and/or many miscellaneous allowances given only to a building which is fully sprinklered per NFPA 13 [such as 403.3, 404.2, 507.3, 507.4, 704.8.1, 717.3.3, 717.4.3, etc.]
Regarding the I-codes, they would not be able to function properly without the codes and standards by NFPA. The reverse is not true regarding NFPA, which doesn't need any ICC codes. David W. S. Blackwell, II, PE, CFI-I, CFPE Engineering ---------------------------------------------------------------- Office of State Fire Marshal 141 Monticello Trail Columbia, SC 29203 Phone: 803.896.9833 Fax: 803.896.9806 Email: [email protected] OSFM Website: http://www.llr.state.sc.us/firemarshal.asp ---------------------------------------------------------------- -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of John Drucker Sent: Monday, January 04, 2010 4:38 PM To: [email protected] Subject: RE: Group 'I' Occupancies Thanks Roland, Also keep in mind that the IBC does not reference NFPA-13, 13R or 13D in 903.2.5 directly from the use group requirements but rather directs the user first to 903.3.1.1, 903.3.1.2 and 903.3.1.3. The IBC does this intentionally in order to stipulate sprinkler requirements from the building code, a prime example is the balcony and deck requirements at 903.3.1.2.1. In other word the IBC gets to say something about these systems BEFORE sending the user to the standard. Hope that helps, John Drucker Jr CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Borough of Red Bank, NJ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Monday, January 04, 2010 4:19 PM To: [email protected] Subject: Re: Group 'I' Occupancies additional translation - 903.3.1.2 is 13R and 903.3.1.3 is 13D As the definition showed, the allowance for a 13D system for an assisted living facility is NOT only for small facilities (ie 5). WE did submit a proposal to tighten up the requirements on whether or not such facilities have to be inspected per NFPA 25 since the 06 and 09 editions IMPLY no such inspections. The problem is that they treat 13D as exclusively applying to only one and two family dwelling and town houses and ignore this exception for I-1. Roland On Jan 4, 2010, at 10:37 AM, John Drucker wrote: > 2006 IBC > > 903.2.5 Group I. An automatic sprinkler system shall be provided > throughout buildings with a Group I fire area. > Exception: An automatic sprinkler system installed in accordance with > Section 903.3.1.2 or 903.3.1.3 shall be allowed in Group I-1 > facilities. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)