Remember that the Architect may not want to use the exception for 13R or
13D in I-1 if he needs to retain the "fully sprinklered per NFPA 13"
status that he made need for many IBC code exceptions/modifications such
as the allowable building area increase [506.3], rating reductions
[508.3.3, Table 601, 708.3], and/or many miscellaneous allowances given
only to a building which is fully sprinklered per NFPA 13 [such as
403.3, 404.2, 507.3, 507.4, 704.8.1, 717.3.3, 717.4.3, etc.]

Regarding the I-codes, they would not be able to function properly
without the codes and standards by NFPA.  The reverse is not true
regarding NFPA, which doesn't need any ICC codes.

 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Monday, January 04, 2010 4:38 PM
To: [email protected]
Subject: RE: Group 'I' Occupancies

Thanks Roland, 

Also keep in mind that the IBC does not reference NFPA-13, 13R or 13D in
903.2.5 directly from the use group requirements but rather directs the
user first to 903.3.1.1, 903.3.1.2 and 903.3.1.3. The IBC does this
intentionally in order to stipulate sprinkler requirements from the
building code, a prime example is the balcony and deck requirements at
903.3.1.2.1. In other word the IBC gets to say something about these
systems BEFORE sending the user to the standard. 

Hope that helps,

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Monday, January 04, 2010 4:19 PM
To: [email protected]
Subject: Re: Group 'I' Occupancies

additional translation - 903.3.1.2 is 13R and 903.3.1.3 is 13D

As the definition showed, the allowance for a 13D system for an assisted
living facility is NOT only for small facilities (ie 5).  WE did submit
a proposal to tighten up the requirements on whether or not such
facilities have to be inspected per NFPA 25 since the 06 and 09 editions
IMPLY no such inspections.  The problem is that they treat 13D as
exclusively applying to only one and two family dwelling and town houses
and ignore this exception for I-1.

Roland


On Jan 4, 2010, at 10:37 AM, John Drucker wrote:

> 2006 IBC
>
> 903.2.5 Group I. An automatic sprinkler system shall be provided 
> throughout buildings with a Group I fire area.
> Exception: An automatic sprinkler system installed in accordance with 
> Section 903.3.1.2 or 903.3.1.3 shall be allowed in Group I-1 
> facilities.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to