Here's the report.
http://www.scribd.com/doc/24417667/Riverview-Report




At 02:45 PM 1/4/2010, you wrote:
>George,
>
>I think this is the fire you're discussing from Wells, NY.  Here's the
>information from the Albany Times-Union on Dec 23.
>
>http://www.timesunion.com/AspStories/story.asp?storyID=880991
>
>I'm still trying to get the entire grand jury report as the link they
>provided isn't complete.
>--
>PARSLEY CONSULTING
>Ken Wagoner, SET
>760.745.6181 voice
>760.745.0537 fax
>[email protected] <mailto:[email protected]> e-mail
>www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>
>
>
>George Church wrote:
> > That "difficult or impossible to evacuate" phrase cost a lot of lives in NY
> > State when a group home was protected (over the contractor's objections) to
> > 13D when numerous residents were difficult or impossible to evacuate and
> > staff couldn't do the impossible. They simply needed more than 10 
> minutes to
> > clear the building and didn't have it.
> >
> > Never heard what happened as penalty for the EOR that reiterated 
> the mistake
> > of 13d when the objection was raised.
> >
> > BROADCASTING THAT PENALTY, if commiserate with the resultant loss 
> of life in
> > the building for what appears to be an obvious failure to properly analyze
> > the protection levels with the residents' needs and staff's 
> abilities, would
> > do more to stop incompetent Professionals from practicing outside 
> their area
> > of competence more than anything else we could do.
> >
> > Anyone in NY know what happened to the bad guy in this one from the recent
> > past? I'd sure like to know. Hopefully it is more than what happened to
> > Dennis the Coverplate Gluer (apologies to Mr Zevon) who is now working for
> > his brother in northern California, I hear, installing sprinklers. There
> > ought to be a way for bad guys to be drummed out of this industry. Like the
> > union activist who capped piping in walls on its way to dorm room
> > sprinklers, so there was no supply to the sprinklers in the rooms, and if
> > there was a fire in the rooms affected by this criminal action, the
> > residents could have died in a room protected by residential sprinklers.
> > That guy, Mr Brian Beyer, should also be prohibited from hanging 
> pipe again.
> > So if you know of Brian and he's hanging pipe, you might want to let his
> > boss know the man has no scruples against raping the integrity of an
> > installation if it suits his purpose. I was told that Brian was not working
> > with any directive from the union to sabotage the installation nor would
> > they have allowed sabotage like this......but it happened, and in more than
> > one room.
> >
> > This certainly doesn't mean small group homes can't be properly protected
> > with 13d- just that the protection level must be commiserate with the risk.
> >
> > glc
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of John Drucker
> > Sent: Monday, January 04, 2010 1:37 PM
> > To: [email protected]
> > Subject: RE: Group 'I' Occupancies
> >
> > 2006 IBC
> >
> > 903.2.5 Group I. An automatic sprinkler system shall be provided
> > throughout buildings with a Group I fire area.
> > Exception: An automatic sprinkler system installed in accordance with
> > Section 903.3.1.2 or 903.3.1.3 shall be allowed in Group I-1 facilities.
> >
> > 308.2 Group I-1. This occupancy shall include buildings,structures or
> > parts thereof housing more than 16 persons, on a 24-hour basis, who
> > because of age, mental disability or other reasons, live in a supervised
> > residential environment that provides personal care services. The
> > occupants are capable of responding to an emergency situation without
> > physical assistance from staff. This group shall include, but not be
> > limited to, the following:
> >
> > Residential board and care facilities
> > Assisted living facilities
> > Halfway houses
> > Group homes
> > Congregate care facilities
> > Social rehabilitation facilities
> > Alcohol and drug centers
> > Convalescent facilities
> > A facility such as the above with five or fewer persons shall
> > be classified as a Group R-3 or shall comply with the International
> > Residential Code in accordance with Section 101.2. A
> > facility such as above, housing at least six and not more than 16
> > persons, shall be classified as Group R-4.
> >
> > So when is an "I-1" not an "I-1" ?  Pay special attention to the
> > operative stipulation; "The occupants are capable of responding to an
> > emergency situation without physical assistance from staff."
> >
> > Hope that helps,
> >
> > John Drucker Jr.
> > Fire Protection Subcode Official
> > Borough of Red Bank, NJ
> >
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Ralphy
> > Henderson
> > Sent: Monday, January 04, 2010 1:10 PM
> > To: [email protected]
> > Subject: Group 'I' Occupancies
> >
> > Are Group i occupancies (10 bed assisted living) considered 13 criteria
> > or 13R?
> >
> > Seeing how it's a group "i" and not an "R" I would say that 13R doesn't
> > apply but what's the consensus here? I've seen some smaller Group I's (5
> > bed or less) considered as 13D when they're hospices that are in a
> > person's home but not 10 bed in a new building.
> >
> >
> > Thanks,
> > RH
> >
> >
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> >
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to