Thanks Craig. I must have read right past that two or three times this
morning. I need a vacation.

Ron

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, January 14, 2010 1:18 PM
To: [email protected]; [email protected]
Subject: RE: In-rack system zoning



8.13 In-Rack Sprinklers.
8.13.1 System Size. The area protected by a single system of
sprinklers in racks shall not exceed 40,000 ft2 (3716 m2) of floor
area occupied by the racks, including aisles, regardless of the
number of levels of in-rack sprinklers. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis
Mack, SET
Sent: Thursday, January 14, 2010 3:15 PM
To: [email protected]
Subject: Re: In-rack system zoning

Ron:

i remember reading the same thing and it did include the rack aisles.  I
will try to find it.

T

On 1/14/2010 1:10 PM, Fletcher, Ron wrote:
> Would the 40,000 sqft limit apply to the area including the aisles? Of

> the 65,000 sqft of area the racks cover only about half is actually 
> rack. So if there is only 32,500 sqft. of rack one system should do
it?
> 13 doesn't address the issue (that I can find) and maybe that's why. I

> thought I read something a few years ago about limiting the size but I

> can't remember where I saw it.
>
> Thanks for the reply,
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Jim Z
> Sent: Thursday, January 14, 2010 12:02 PM
> To: [email protected]
> Subject: Re: In-rack system zoning
>
> The way I understand it 40,000 sf is your limit.
> *
> 8.2.1 *The maximum floor area on any one floor to be protected by 
> sprinklers supplied by any one sprinkler system riser or combined 
> system riser shall be as follows:
> (3) Extra hazard
> (a) Pipe schedule - 25,000 ft2 (2323 m2)
> (b) Hydraulically calculated - 40,000 ft2 (3716 m2)
> (4) Storage-High-piled storage (as defined in 3.9.1.13) and storage 
> covered by other NFPA standards - 40,000 ft2 (3716 m2)
>
> *3.9.1.13 *High-Piled Storage. Solid-piled, palletized, *rack 
> storage*, bin box, and shelf storage in excess of 12 ft (3.7 m) in 
> height.
>
> -Jim
>
> On Thu, Jan 14, 2010 at 11:48 AM, Fletcher, Ron
> <[email protected]>wrote:
>
>    
>> We have 65,000 sqft of rack storage that requires in-rack sprinklers.
>> The racks span an area that is protected by 4 roof systems. Can we 
>> use
>>      
> a
>    
>> single system to supply the in-rack and have all 65,000 sqft on a
>>      
> single
>    
>> valve?
>>
>> I thought that I read somewhere once upon a time that in-rack systems

>> had to be zoned similar to roof systems i.e. 40,000 sqft max etc...
>>
>> Ron Fletcher
>> Aero Automatic
>> Phoenix, AZ
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>>      
> to:[email protected]<to%3ASprinklerforum-reques
> t@
> firesprinkler.org>
>    
>> (Put the word unsubscribe in the subject field)
>>
>>      
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>    


--
Please feel free to call if you have any questions or comments.

Sincerely,

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
Office (480) 505-9271
Fax (866) 430-6107

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to