craig,
Good find. I just found that and almost hit send

-Jim

On Thu, Jan 14, 2010 at 2:18 PM, <[email protected]> wrote:

>
>
> 8.13 In-Rack Sprinklers.
> 8.13.1 System Size. The area protected by a single system of
> sprinklers in racks shall not exceed 40,000 ft2 (3716 m2) of floor
> area occupied by the racks, including aisles, regardless of the
> number of levels of in-rack sprinklers.
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Travis Mack, SET
> Sent: Thursday, January 14, 2010 3:15 PM
> To: [email protected]
> Subject: Re: In-rack system zoning
>
> Ron:
>
> i remember reading the same thing and it did include the rack aisles.  I
> will try to find it.
>
> T
>
> On 1/14/2010 1:10 PM, Fletcher, Ron wrote:
> > Would the 40,000 sqft limit apply to the area including the aisles? Of
> > the 65,000 sqft of area the racks cover only about half is actually
> > rack. So if there is only 32,500 sqft. of rack one system should do it?
> > 13 doesn't address the issue (that I can find) and maybe that's why. I
> > thought I read something a few years ago about limiting the size but I
> > can't remember where I saw it.
> >
> > Thanks for the reply,
> >
> > Ron Fletcher
> > Aero Automatic
> > Phoenix, AZ
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Jim Z
> > Sent: Thursday, January 14, 2010 12:02 PM
> > To: [email protected]
> > Subject: Re: In-rack system zoning
> >
> > The way I understand it 40,000 sf is your limit.
> > *
> > 8.2.1 *The maximum floor area on any one floor to be protected by
> > sprinklers supplied by any one sprinkler system riser or combined
> > system riser shall be as follows:
> > (3) Extra hazard
> > (a) Pipe schedule - 25,000 ft2 (2323 m2)
> > (b) Hydraulically calculated - 40,000 ft2 (3716 m2)
> > (4) Storage-High-piled storage (as defined in 3.9.1.13) and storage
> > covered by other NFPA standards - 40,000 ft2 (3716 m2)
> >
> > *3.9.1.13 *High-Piled Storage. Solid-piled, palletized, *rack
> > storage*, bin box, and shelf storage in excess of 12 ft (3.7 m) in
> > height.
> >
> > -Jim
> >
> > On Thu, Jan 14, 2010 at 11:48 AM, Fletcher, Ron
> > <[email protected]>wrote:
> >
> >
> >> We have 65,000 sqft of rack storage that requires in-rack sprinklers.
> >> The racks span an area that is protected by 4 roof systems. Can we
> >> use
> >>
> > a
> >
> >> single system to supply the in-rack and have all 65,000 sqft on a
> >>
> > single
> >
> >> valve?
> >>
> >> I thought that I read somewhere once upon a time that in-rack systems
> >> had to be zoned similar to roof systems i.e. 40,000 sqft max etc...
> >>
> >> Ron Fletcher
> >> Aero Automatic
> >> Phoenix, AZ
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> >>
> > to:[email protected]<to%[email protected]>
> <to%3ASprinklerforum-reques
> > t@
> > firesprinkler.org>
> >
> >> (Put the word unsubscribe in the subject field)
> >>
> >>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
>
>
> --
> Please feel free to call if you have any questions or comments.
>
> Sincerely,
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> Office (480) 505-9271
> Fax (866) 430-6107
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to