After you consult with the engineer......... Perhaps weld the legs to the inside of the containment, weld brackets to the outside of the containment, attach the brackets to the floor. The rigidity of the tank must be sufficient to carry the tank force to the angle brackets and the floor.
Perhaps someone makes a double wall factory tank similar to a Roth. http://www.roth-usa.com/usa/pdf/DWT1000_02-06.pdf John Drucker -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Tuesday, January 19, 2010 8:18 AM To: [email protected] Subject: Pump Fuel Tank Mounting We are installing a diesel fire pump package. Normally we have 2" legs with floor flanges screwed to the bottom for mounting the diesel fuel tank to the floor, and they pour concrete curbing for a dike. This project, the insurance company wanted a steel dike on the floor with the tank in it. Does anyone have a suggestion for mounting the tank? If we mount the floor flanges the anchors will have to penetrate the dike. Thank you in advance. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)