Yep, found some guidance in the FM sheets.
Thanks to all.
Dewayne 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Friday, January 22, 2010 10:36 AM
To: [email protected]
Subject: Re: Exposed Expanded Group A Plastics

slow down.  AS others have identified, FM Loss Prevention Data sheets provide 
guidance for spray sprinklers

Roland

On Jan 22, 2010, at 8:25 AM, Matt Grise wrote:

> I think what the decision tree suggests is that the arrangement of 
> exposed, expanded, group A plastic on a rack is pretty much guaranteed 
> to burn up uncontrollably...even with sprinklers. They may want to 
> look into a different storage arrangement. (solid shelves would put 
> them into chap 15)
>
> Also of note is A20.2 (13-2007):
>
> "Exposed, expanded plastic... ...This test commodity used in the 
> large-scale sprinklered fire test proved to be the worst challenge..."
>
> Matt Grisé PE*, LEED AP