Check FM first, then get an FPE or AHJ decision on protection requirement.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, January 22, 2010 9:14 AM
To: [email protected]
Subject: Exposed Expanded Group A Plastics

 I am having a problem coming up with design criteria for the following
using NFPA 13 (07ed). 
 
Product:   Exposed, Expanded, Group A plastic Foam Taxidermy forms (the
type used for target shooting)  in open shelf racks stored to 12' in a 20'
high building.  Aisle width is 4'.  
Total storage is around 40,000 SF.
Since the storage is over 5ft and 4000SF, this puts us out of miscellaneous
storage.  When I use the decision tree in chapter 17, it tells me that I am
outside the scope of ch17.
Any suggestions?
Thanks,
Dewayne