Good Morning members:

 

Got a question about combustible concealed space:  I have a building that
has a roof structure built of 20" deep combustible barjoist (2x4 top and
bottom chords with steel tubing for webs) with a plywood roof deck and
ceiling.  The GC was originally going to fill trusses entirely full of
fiberglass insulation (bats) thus nullifying the sprinkler requirement per
NFPA 13 (2002) 8.14.1.2.7, now he must provide an air gap to allow the space
to breathe. If the air gap is 4" or less is there a requirement to protect
this space, since it's no longer in compliance with 8.14.1.2.7?  I would
suspect it is still ok to keep it unprotected by using 8.14.1.2.4 since we
are less than 6"?  Any thoughts?  

 

Jim Johnston, P.E.

Fire Protection Engineer

Inland Fire Protection, Inc