Burton, 

Yes the inspector is since the inspector must override the disconnect
interlock to open the panel door in the energized condition and or energize
the controller with the door open. The potential (operating voltage) is a
key criteria in arc flash severity and personal protection.

2009 NFPA-70E provides; Arc Flash Hazard. A dangerous condition associated
with the possible release of energy caused by an electric arc. 

FPN No. 1: An arc flash hazard may exist when ENERGIZED ELECTRICAL
CONDUCTORS OR CIRCUIT PARTS ARE EXPOSED or when they are within equipment in
a guarded or enclosed condition, provided a person is interacting with the
equipment in such a manner that could cause an electric arc. UNDER NORMAL
OPERATING CONDITIONS, ENCLOSED ENERGIZED EQUIPMENT that has been properly
installed and maintained is not likely to pose an arc flash hazard. 

FPN No. 2: See Table 130.7(C)(9) for examples of activities that could pose
an arc flash hazard.  

130.7(C)(9)

Panelboards or Other Equipment Rated 240 V and Below    Work on energized
electrical conductors and circuit parts, including voltage testing Risk
Category  1

Panelboards or Switchboards Rated >240 V and up to 600 V (with molded case
or insulated case circuit breakers)  Work on energized electrical conductors
and circuit parts, including voltage testing Risk Category  2

600 V Class Motor Control Centers (MCCs) Work on energized electrical
conductors and circuit parts, including voltage testing Risk Category  2

(10) Protective Clothing and Personal Protective Equipment Matrix. Once the
Hazard/Risk Category has been identified from Table 130.7(C)(9) (including
associated
notes) and the requirements of 130.7(C)(9), Table 130.7(C)(10) shall be used
to determine the required PPE for the task.

Hazard/Risk Category 1
FR Clothing, Minimum Arc Rating of 4 (Note 1) Arc-rated long-sleeve shirt
(Note 3)
Arc-rated pants (Note 3)
Arc-rated coverall (Note 4)
Arc-rated face shield or arc flash suit hood (Note 7)
Arc-rated jacket, parka, or rainwear (AN)
FR Protective Equipment Hard hat
Safety glasses or safety goggles (SR)
Hearing protection (ear canal inserts)
Leather gloves (Note 2)
Leather work shoes (AN)

Hazard/Risk Category 2
FR Clothing, Minimum Arc Rating of 8 (Note 1) Arc-rated long-sleeve shirt
(Note 5)
Arc-rated pants (Note 5)
Arc-rated coverall (Note 6)
Arc-rated face shield or arc flash suit hood (Note 7)
Arc rated jacket, parka, or rainwear (AN)
FR Protective Equipment Hard hat
Safety glasses or safety goggles (SR)
Hearing protection (ear canal inserts)
Leather gloves (Note 2)
Leather work shoes

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ford, Charles
Sent: Tuesday, January 26, 2010 10:15 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Electrical Dangers

A question has come up regarding electric fire pump testing. During the
required voltage and amperage
tests, is the inspector exposed to harm from high voltage electricity. If
the answer is YES, do you,
(they etc.) provide high voltage protective gear and tools in accordance
with NFPA 70E?

C. Burton Ford
Designer- NICET Certified: Fire Alarm, 
Special Hazards, Sprinkler Design 
&Sprinkler Inspections
NFPA CFPS
Cintas Fire Protection-D-47
Warminster, PA 18974
Phone 267-487-1000
Fax 267-487-1010


This e-mail transmission contains information that is intended to be
confidential and privileged.  If you receive this e-mail and you are not a
named addressee you are hereby notified that you are not authorized to read,
print, retain, copy or disseminate this communication without the consent of
the sender and that doing so is prohibited and may be unlawful.  Please
reply to the message immediately by informing the sender that the message
was misdirected.  After replying, please delete and otherwise erase it and
any attachments from your computer system.  Your assistance in correcting
this error is appreciated.  
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to