We've got a problem child project where sand in the water supply clogs up
the cooling jacket on the diesel, and sand blasts the rubbers in valves so
they drip.

Small private water purveyor (the developer of the industrial park is the
owner) supplies our diesel which then feeds the systems, all interior piping
downstream of pump. Project located several miles from the ocean, a couple
miles from the Bay.

I can't imagine a strainer with perfs small enough to grab grains of sand
and not have atrocious friction loss. I can't find cheesecloth to wrap
around the strainer basket that's UL-Listed in a pump suction application.

While I haven't encountered this before, it likely isn't the first time the
problem has been encountered. Any one know a remedy other than a tank (with
settling basin?) and higher pressure 2,500 GPM pump to make up for the loss
of city residual pressure?

George Church
Rowe Sprinkler