It really depends on the location of the fire plume in relationship to the
heads and where the jet will be directed by the roof/ceiling elements.  When
I said the AHJ "may" have a point.  I was responding in the hypothetical.
It the original post the second head would have been 10' away from the first
beam and 19' away from the wall.  Since fire plumes go straight up and then
outward, if the fire were 11' feet away from the wall, two feet away from
the first beam, chances are the first head located on the other side of the
beam which is covering that part of the floor would not fuse.  I assumed
that there were more heads spaced along in the same beam pockets all spaced
the same distance away from the wall.  My guess is the row of heads 19 feet
away from the wall and 8' away from the fire plume in the second beam pocket
would all fuse before the head that is only six feet away.  We also don't
know what's past the second beam-since he said beam and not wall, what's
happening past that point.  I would need to see the plans to know what I
really felt.  My point is that just because you meet deflector distance (I
do realize that his deflectors are less than 12" per the unobstructed rules)
and obstruction rules, based on 8.1.1 and the fact that NFPA 13 doesn't
address heads above the bottom of beams in unobstructed construction, your
design may still be deficient when you look at the head layout in relation
to fire sprinkler performance theory.  
 
As sprinkler designers, we often fall into the trap of thinking covering the
floor area is what is most important.  It is very important to look at our
designs with regard to response time as well.  Where will the heat go when
there is a fire?  Unfortunately, fires don't always start directly below our
sprinkler heads. Unless there is a breeze in the building, the heat will go
straight up and then outward from there.  If there is nothing to cause it to
collect it will follow the path of least resistance.  It doesn't care if
there is a sprinkler head 6 feet away on the other side of a beam.  It might
as well be a wall.  
 
Personally, I would ere on the side of caution and space to the beams in
this case. 
 
Mike Ricks
Katco Fire Sprinkler Design
 
Interesting analysis and welcome to the jungle. However, if you read 
the handbook commentary it would seem that your concern about ceiling 
jets is addressed in the definitions of obstructed and unobstructed 
construction. I am far from an expert on the behavior of ceiling 
jets, but I would think in this situation as described, that the 
sprinklers as positioned, especially in a 17 ft span, would be within 
that jet.
 
 
At 09:52 PM 2/10/2010, you wrote:
>Not to be the contrarian here, this being my first post to this forum, but,
>I believe the AHJ has a point.
> 
> 
> 
>Given your beam spacing of over 7'-6" on center, you are dealing with
>unobstructed construction here.  NFPA 13 8.6.4.1.2, regarding placing the
>deflector above the bottom of the structural member, relates to obstructed
>construction.  In obstructed construction, we are able to place deflectors
>up to 22" below roof decks since the obstructions help collect heat to
>assure prompt activation of the sprinkler head.  (If you remember your
older
>versions of NFPA 13, we used to have to deal with the "panelized roof
>limitations of 300 square feet to get the added deflector distance.)  NFPA
>13 doesn't specifically address the issue of placing the deflector above
the
>beam in unobstructed construction and although you are meeting the
>obstruction requirements of 8.6.5.1.2, the issue here is response time.
>8.1.1 (2) states "Sprinklers shall be positioned and located so as to
>provide satisfactory performance with respect to activation time and
>distribution."  A8.1 also says "The installation requirements are specific
>for the normal arrangement of structural members.  There will be
>arrangements of structural members not specifically detailed by the
>requirements."  Just because your head is not obstructed and you have met
>the deflector distance requirements for unobstructed construction doesn't
>mean it will work as intended.
> 
> 
> 
>The theory behind automatic sprinkler performance requires that the head be
>in the jet stream or in a pocket that will collect heat in a timely manner.
>With limited obstructions to collect heat, that distance will be 5 to 12%
of
>the height of the ceiling above the fire source.   This is the theory
behind
>the 12" deflector distance rule for unobstructed construction.  Given the
>language of NFPA A8.1 and 8.1.1 the AHJ is not off base in being concerned
>with response times.  Unless you have a 30'+ ceiling, I would have concerns
>that the jet stream would be cut off by the beams and that the heat would
>not collect fast enough to assure prompt activation of the head and/or
>skipping would occur causing head outside of the fire area to activate
prior
>to heads in and around the fire area due to the jet stream being directed
>away from those heads by the beams.
> 
> 
> 
>Michael Ricks
> 
>Katco Fire Sprinkler Design
> 
>P.O. Box 607
> 
>555 South 100 East
> 
>Salem, UT   84653
> 
>801-423-3096  Cell:  801-380-4651
> 
>mike at fire-sprinkler-design.com
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
> 
> 
> 
> 
> 
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum at firesprinkler.org
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
>For Technical Assistance, send an email to: support at firesprinkler.org
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
> 
>To Unsubscribe, send an email to:Sprinklerforum-request at
firesprinkler.org
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
>(Put the word unsubscribe in the subject field)
 
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  

 

 

Michael Ricks

Katco Fire Sprinkler Design

P.O. Box 607

555 South 100 East

Salem, UT   84653

801-423-3096  Cell:  801-380-4651

[email protected]

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to