So if you back out the drop with the sprinkler on it and don't touch 
the sprinkler, it is OK to put it back?


At 10:45 AM 2/24/2010, you wrote:
>Good point.  The way I look at the intent is IF you put a wrench on
>the sprinkler, it's a good idea to replace it.
>
>Roland
>
>On Feb 24, 2010, at 4:37 AM, <[email protected]> wrote:
>
> > All the AHJ's in my area (Atlanta) have always accepted the
> > relocation of an existing sprinkler as long as you don't remove it
> > from the fitting to which it is attached.
> >
> > Lamar Vaughn
> > Vaughn & Company
> >
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to