If you asking how far a FDC be located from a hydrant, then the answer
is as follows:

 

NFPA 13 - Does not have a requirement.

NFPA 14 - Has a requirement.  6.4.5.4:  Fire department connections
shall be located not more than 100 ft (30.5 m) from the nearest fire
hydrant connected to an approved water supply.

 

Hope this helps,

John

 

 

John August Denhardt, P.E.

Strickland Fire Protection Incorporated

5113 Berwyn Road

College Park, Maryland 20740

Office Telephone Number:  301-474-1136

Mobile Telephone Number:  301-343-1457

FIRE SPRINKLERS SAVE LIVES 

 

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
Gillett
Sent: Monday, March 08, 2010 9:53 AM
To: [email protected]
Subject: FDC LOCATION

 

Can anyone call out the code from NFPA that says hydrants are to be
spaced

within 100'-0 of a hydrant unless approved by AHJ? I have searched for
and

am not finding it.

 

 

 

Thank you in adavance.

 

 

 

Bobby Gillett

 

Sr. Project Manager

 

Key Fire Protection, Inc.

 

(731) 424-0130 office  (731) 424-9285 fax 

 

(731) 267-4853 cell

 

 <mailto:[email protected]>

[email protected]

 

 

 

 

 

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 

For Technical Assistance, send an email to: [email protected]

 

To Unsubscribe, send an email
to:[email protected]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to