Ed,

2006 IPC  608.16.4.1 Additives or nonpotable source.

Where systems under continuous pressure contain chemical additives or 
antifreeze, or where systems are connected to a nonpotable secondary water 
supply, the potable water supply shall be protected against backflow by a 
reduced pressure principle backflow preventer. Where chemical additives or 
antifreeze are added to only a portion of an automatic fire sprinkler or 
standpipe system, the reduced pressure principle backflow preventer shall be 
permitted to be located so as to isolate that portion of the system. Where 
systems are not under continuous pressure, the potable water supply shall be 
protected against backflow by an air gap or a pipe applied atmospheric vacuum 
breaker conforming to ASSE 1001 or CSA B64.1.1.


I don't see any exceptions??  Hope this helps.


Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:    Emails from this company normally contain 
confidential and privileged material, and are for the sole use of the intended 
recipient.  Use or distribution by an unintended recipient is prohibited, and 
may be a violation of law.  If you believe that you received this in error, 
please do not read the body of this e-mail and please inform the sender that 
you have deleted the e-mail and any copies.  Thank you.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Thursday, March 11, 2010 10:23 AM
To: [email protected]
Subject: Backflow protection on antifreeze system

Anybody have a 2006 International Plumbing Code handy?



I have a client who wants to use glycerine in a small antifreeze system.
Nothing unusual about that.   But he claims that by using food-grade
glycerine he doesn't need an RP BFP and the associated expansion tank.  I
disagree,  but don't have code references to back it up.   The 2006 IPC is
applicable.



Thanks in advance!



Ed Kramer

Kramer Design, LLC

Littleton, CO

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to