No. But if the building is required to be sprinklered throughout it may need to have sprinklers within the room as well as the FM-200. In some cases Architects may opt to have sprinklers installed in order to take advantage of certain allowances for height or area. If they use the sprinkler inclusion for that purpose in most cases the AHJ's won't allow omission of sprinklers.
But preaction isn't a requirement by Code or Standard. It may be a client or Insurance recommendation or requirement as opposed to using a wet pipe system. But according to NFPA 13, if you are going to substitute FM-200 (or any other non-sprinkler type system) for sprinklers it must be approved by the AHJ. So you'll have some phone calls to make. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brian Harris Sent: Wednesday, March 24, 2010 7:48 AM To: [email protected] Subject: FM-200 System Is a pre-action system required when an FM-200 system is installed? Thanks in Advance, Brian _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)