Remember that the building code requires the building to be sprinklered 
throughout and the use of alternative fire suppressions systems instead of 
sprinkler systems does not met the requirements of the building code. Be very 
careful if the building is classified as an unlimited area building under the 
building code because the substitution of a clean agent system for the code 
required sprinkler system would violate the large area building protection 
requirements of the building code. The owner has no choice but to comply with 
the building code. I have seen a few building code officials shut down large 
area buildings because the IT manager had the sprinkler system removed from the 
IT server room and replaced with a clean agent system. The building code 
official has the last word when it comes to the building being "sprinklered 
throughout".  

Have a fire safe day!

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Wednesday, March 24, 2010 9:45 AM
To: [email protected]
Subject: RE: FM-200 System

Further to this is a requirement that technical documentation shall be
furnished to the AHJ.

Interesting when you're looking at a clean agent in lieu of a sprinkler
system.

Has anyone developed a technical documentation indicating this arrangement
is equal or better than sprinkler protection, for those with a customer who
is hydrophobic?

Our AHJ isn't saying he won't accept it, and in a small 10x12 IT room in a
100,000 SF light hazard building, it's not a mountain, it's a molehill. BUT-
you still need to submit technical documentation for a molehill.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, March 24, 2010 8:37 AM
To: [email protected]
Subject: RE: FM-200 System

2006 IBC/IFC

[F] 904.2 Where required. "Automatic fire-extinguishing systems
installed as an alternative to the required automatic sprinkler systems
of Section 903 shall be approved by the fire code official. Automatic
fire-extinguishing systems shall not be considered alternatives for the
purposes of exceptions or reductions allowed by other requirements of
this code."

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian
Harris
Sent: Wednesday, March 24, 2010 7:48 AM
To: [email protected]
Subject: FM-200 System


 Is a pre-action system required when an FM-200 system is installed?

Thanks in Advance,
Brian






_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)




CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity
to which it is addressed and may contain information that is privileged and
confidential, nor is it, unless specifically stated, intended to be relied
upon by any person or persons other than the individual or entity named
above and no warranties or representations are made or intended to persons
or entities not named above.  If the reader is not the intended recipient,
you are hereby notified that any dissemination, distribution or copying of
this communication is strictly prohibited.  If you have received this
communication in error, please notify us immediately by telephone, return
this message to the address above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to