It was also amended by the 2004 IBC Supplement to IBC 2003, and the 2007 IBC
Supplement to IBC 2006

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, March 25, 2010 3:57 PM
To: [email protected]
Subject: RE: Seismic Restraint Standards

What edition of ASCE are you referring to as "the latest"?    To my
knowledge, the 2005 is the latest and sections 13.6.8.2 and 13.6.8.3 speak
directly to the "exclusion" as you call it.   The 2007 edition of NFPA 13
included revisions, specifically tables 9.3.5.3.2(a) and (b), as well as
Table 9.3.5.6.2 and the associated steps in the calculation procedure, that
meet the prescribed "force and displacement requirements of Section 13.3.1
and 13.3.2", if I'm not mistaken.   All that taken together means that a
system designed with seismic bracing in accordance with NFPA 13, 2007 or
2010 editions in fact DOES meet ASCE 7, and in turn the requirements of
Chapter 16 of all IBC editions up to and including 2009.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Thursday, March 25, 2010 1:37 PM
To: [email protected]
Subject: RE: Seismic Restraint Standards

TO all;

The IBC refers to ASCE 7 as the Standard for earthquake bracing, if I
remember correctly the ASCE 7 standard in effect at the time of the adoption
of the 2003 IBC specifically excluded NFPA 13 as a standard for earthquake
bracing through the reference in ASCE 7 excluding NFPA 13 seismic bracing
since NFPA 13 requirements did not meet the requirements of  ASCE 7. In the
latest edition of ASCE 7 the NFPA 13 seismic bracing exclusion was removed
from ASCE 7. Be aware of the version of the IBC that is being enforced in
your area of operation since the IBC is considered the legal code which
tells the designer, owner and design professionals what the requirements are
for the building based on occupancy, construction type, ground floor area,
building height and exposure to building.       

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, March 25, 2010 3:46 PM
To: [email protected]
Subject: RE: Seismic Restraint Standards

We get those cross referenced type specs now and then.

For mechanical piping, plumbing, duct, etc, SMACNA.

For Fire Protection,  NFPA 13. SMACNA isn't referenced in the NFPA
INSTALLATION Standard, because 13 has it's own rules to follow.  

SMACNA is also no longer referenced in the IBC as of the 2003 edition.  ASCE
7 was established as the accepted standard.  However there was some verbiage
placed in the Code which would permit acceptance of other design standards
if approved by the AHJ.

So if the MEOR wants to apply SMACNA to Mechanical piping and duct systems
he needs to request permission from the AHJ to use that standard.

But as previously stated,  NFPA 13 is the applicable standard for design of
seismic bracing for Fire Protection service piping not SMACNA.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Cyr
Sent: Thursday, March 25, 2010 3:01 PM
To: American Fire Sprinkler Association
Subject: Seismic Restraint Standards

Forumites:

General Mechanical specs often refer to SMACNA for seismic restraint of
piping systems. Sprinkler specs often refer to General Mechanical.

Question: Does NFPA 13 seismic bracing requirements take precedence over
SMACNA?

How was the battle won with the MEOR when he says SMACNA is the preferred
standard for bracing of piping systems?

Any comments would be appreciated.

Thank you,
Ed Cyr

*Alpha Fire Sprinkler Corp.*
San Luis Obispo, CA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature
database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature
database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to