Per NFPA 24 NFPA 24, Standard for the Installation of Private Fire Service 
Mains and Their Appurtenances, 2010 Edition

Chapter 10: 


10.3.1 Threaded Pipe and Fittings.   All threaded steel pipe and fittings shall 
have threads cut in accordance with ASME B1.20.1.


10.3.2 Groove Joining Methods.   Pipes joined with grooved fittings shall be 
joined by a listed combination of fittings, gaskets, and grooves.

10.8.1 General.   

10.8.1.1*    All tees, plugs, caps, bends, reducers, valves, and hydrant 
branches shall be restrained against movement by using thrust blocks in 
accordance with 10.8.2 or restrained joint systems in accordance with 10.8.3.



10.8.1.2    Piping with fused, threaded, grooved, or welded joints shall not 
require additional restraining, provided that such joints can pass the 
hydrostatic test of 10.10.2.2 without shifting of piping or leakage in excess 
of permitted amounts.



10.8.1.3 Steep Grades.   On steep grades, mains shall be additionally 
restrained to prevent slipping.


10.8.1.3.1    Pipe shall be restrained at the bottom of a hill and at any turns 
(lateral or vertical).



10.8.1.3.2    The restraint specified in 10.8.1.3.1 shall be to natural rock or 
to suitable piers built on the downhill side of the bell.



10.8.1.3.3    Bell ends shall be installed facing uphill.



10.8.1.3.4    Straight runs on hills shall be restrained as determined by the 
design engineer.

FRANK J. HERRICK
CITY OF LEAWOOD FIRE DEPARTMENT  
OFFICE OF THE FIRE MARSHAL
14801 MISSION ROAD
LEAWOOD, KS. 66224-9560
OFFICE:        913.681.6788 x 26 
FAX:              913.681.2399
-----Original Message-----
From: Greg McGahan [mailto:[email protected]] 
Sent: Thursday, March 25, 2010 4:00 PM
To: [email protected]
Subject: RE: Grooved Underground, Thrust Blocks Required?


In the past when I have checked, I was told in no uncertain times that Grooved 
fittings are NOT listed for UG use.

Greg McGahan

Living Water Fire Protection
 (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Thursday, March 25, 2010 1:36 PM
To: [email protected]
Subject: Grooved Underground, Thrust Blocks Required?

A quick question about galvanized steel underground...

Galvanized 3", about 80 ft, grooved fittings...
Would this require thrust blocks?

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to