Something further if you are contemplating the 2009 IBC provisions for Live / Work units in Section 419 ...
Aside from the specific sprinkler design issues cited you should be aware that 419.11 #3 prohibits the non-residential use from being on any level other than the first / main floor ..... did someone mention this office was in the basement? Additionally, if the Live Work unit is applied it makes the entire building a Group R-2 which triggers fire sprinkler protection which we already are talking about and the system is also required to be supervised to the IBC Section 907.2.9. All of this is theoretical though if the prevailing building code in the jurisdiction is not the 2009 IBC ... just my thoughts on not getting into which referenced standard applies until after passing through the adopted building code which may very well make that decision and others for us in advance. Dave Phelan _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)