If your moving product through this oven it's a moving target and
where will the threat be when the water arrives or will you too many
heads open? If it's not moving isn't the entire enclosure equally
threatened? Am I seeing something that's bigger than what's actually
there?

On Mon, Mar 29, 2010 at 1:04 PM,  <[email protected]> wrote:
> I've used CO2 and Dry Chem. also used high-speed deluge (14 ms reaction from 
> UV detection to discharge) on material handling ovens where you've got 
> product moving through the oven.   It all just depends on the application.  
> It really depends on the product and how it reacts to different suppression 
> elements.  Some stuff you just don't put water on.
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Monday, March 29, 2010 4:00 PM
> To: [email protected]
> Subject: Re: 500 DEGREE OVEN
>
> Now this makes more sense to me. I think Craig's CO2 (although I usually hate 
> the evoking of the term CO2 I doubt if you'll have any air breathers in the 
> area of protection) idea is sound, or perhaps open deluge with the same 
> detection or a Protectowire type product.
>
> On Mon, Mar 29, 2010 at 12:52 PM, Robert Thompson <[email protected]> 
> wrote:
>> Curing oven, combustible product combustible coating. In large quantity 
>> continuous process.
>>
>>
>> Thank you
>>  Robert  Thompson
>>
>>  DAKOTA
>> FIRE PROTECTION
>> 1710 N. Washington Street
>> Grand Forks ND 58206-5327
>> Phone # (701) 772-8820
>> Fax # (701) 772-7932
>> Email [email protected]
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Ron
>> Greenman
>> Sent: Monday, March 29, 2010 2:48 PM
>> To: [email protected]
>> Subject: Re: 500 DEGREE OVEN
>>
>> I'm feeling a little stupid. Why would you need to protect an oven?
>> What kind of oven? What has to heated to 500 degrees that be in a contained 
>> vessel? Isn't this an enclosed space where the fire would be more than less 
>> controlled by the consumption of oxygen? Presumably the oven itself isn't 
>> fuel so what's in it that;'s so hazardous? I really can't figure this one 
>> out.
>>
>> On Mon, Mar 29, 2010 at 12:43 PM, Forest Wilson <[email protected]> 
>> wrote:
>>> Probably because sprinkler water would reach temperatures in excess
>>> of
>>> 120*
>>> (7.7.1.3.1.1) That pertains to combination systems, but I think
>>> there's a similar requirement for standard wet systems.
>>>
>>>
>>> Forest Wilson
>>>
>>> Project Manager
>>> Cherokee Fire Protection Co.
>>> 1855 Bellbrook Ave Ste C
>>> Xenia OH 45385
>>>
>>> PH 937-376-2333
>>> FX 614-455-4324
>>>
>>> visit our blog: www.cherokee-fire.blogspot.com
>>>
>>>
>>> NOTICE: The information contained in this email is intended to be
>>> solely for the use of the named individual or entity to which it is
>>> directed and may contain information that is privileged or otherwise
>>> confidential. It is not intended for transmission to, or receipt by,
>>> anyone other than the named addressee (or a person authorized to
>>> deliver it to the named addressee). It should not be copied or
>>> forwarded to any unauthorized persons. If you have received this
>>> electronic mail transmission in error, please delete it from your
>>> system without copying or forwarding it, and notify the sender of the
>>> error by reply email or by calling Cherokee Fire Protection Co. at
>>> 888-347-3079 toll free.
>>>
>>>
>>>
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Robert
>>> Thompson
>>> Sent: Monday, March 29, 2010 3:36 PM
>>> To: [email protected]
>>> Subject: 500 DEGREE OVEN
>>>
>>> Has anyone had a problem with installing a wet sprinkler in a high temp.
>>> oven approx. 500 degrees.  The piping is on the exterior and a drop
>>> sprinkler into the oven.   An FM plan reviewer stated that FM
>>> suggests using a dry system when temps run this high.
>>>
>>>
>>> Thank you
>>>  Robert  Thompson
>>>
>>>  DAKOTA
>>> FIRE PROTECTION
>>> 1710 N. Washington Street
>>> Grand Forks ND 58206-5327
>>> Phone # (701) 772-8820
>>> Fax # (701) 772-7932
>>> Email [email protected]
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering
>> Bates Technical College
>> Tacoma, WA
>>
>> Member:
>> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________