I'm merely asking 'cause I didn't look anything up and I don't even
have an opinion but if your TJIs are blocked and compartmentalized to
the 164 cuft (again, I didn't look anything up but think that's the
number) would that then eliminate the 3000 sqft design area rule?

On Tue, May 4, 2010 at 11:00 AM, A.P.Silva <[email protected]> wrote:
> My question is:
>
> For the 3000 ft2 design, do I need to (1) include all QR and RES heads in
> the 3000 ft2 area. Or (2) do I need to go to the full 3000, regardless of
> the "length" of the design area to include only QR heads? Or (3) include
> only QR heads up to the "length" of the 3000 sq.ft. not necessarily the full
> 3000 sq.ft.
>
> By "length" I mean the 1.2x sq.rt. Of 3000 sf.
>
> Tony
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Thom McMahon
> Sent: April 3, 2010 10:33 AM
> To: [email protected]
> Subject: RE: Residential sprinklers
>
> Tony:
> 11.2.3.1.4 Restrictions. Regardless of which of the two methods
> (density/area or room design method) is used, the following restrictions
> shall apply:
> (3)*Unless the requirements of 11.2.3.1.4(4) are met for buildings having
> un-sprinklered combustible concealed spaces, as described in 8.15.1.2 and
> 8.15.6, the minimum area of sprinkler operation for that portion of the
> building shall be 3000 ft2 (279 m2). The design area of 3000 ft2
> (279 m2) shall be applied only to the sprinkler system or portions of the
> sprinkler system that are adjacent to the qualifying combustible concealed
> space.
>
> I'd say that since Residential head design is not "Room Design" it does not
> need to meet the room design criteria if you're using residential listed
> heads. (4 Head design) When you switched from res. Heads to the QR heads for
> your "other rooms"
> your back to room design, and must meet 11.2.3.1.4(3)
>
> I spend a lot of time teaching AHJ's , that as soon as you see tji's you
> need to start looking for a 3000 SF remote area, and if you don't see one
> you need to look closely as to why you don't see one. Res. Heads will get
> you out of it in res. Occupancies, but only where they are allowed.
>
> Don't forget the tail end of (3) says "The design area of 3000 ft2
> (279 m2) shall be applied only to the sprinkler system or portions of the
> sprinkler system that are adjacent to the qualifying combustible concealed
> space."
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> Subject: RE: Residential sprinklers
>
> In the other rooms I'm using non-res heads and calculating all heads in such
> rooms that are adjacent to each other. This works out to about 12 heads,
> less than 3000 sf. I hope I don't have to extend the design area to the
> corridors and patient rooms to get up to 3000 sf, as the different k factors
> would create havoc.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to